Mr. Serious
Senior Member
- Location
- Oklahoma, USA
- Occupation
- Electrical Contractor
Sorry, I brought up too many issues and confused everyone. The problem is just that the breaker won't reset. However, before I replace with a new one, I want to also make sure we have the shunt trip voltage applied properly. The site is a 1 hour drive the opposite direction from everywhere else I normally go, so I have not taken the time to go down there and verify if the shunt trip voltage is momentary or continuous.
Checking to make sure the shunt coil doesn't have voltage when trying to reset the breaker: yes, we did that. I had someone disconnect the shunt wires completely, and it still wouldn't reset.
Here is what I'm going to do: I'm going to ask the supplier nicely if they'll cover a replacement, and if not I'll buy a new one. The issue of fault current only came up because I was thinking I might buy a lower-rated one to save money. But I prefer to keep the panels fully rated to 22k as they are now, instead of installing one lower-rated breaker.
Checking to make sure the shunt coil doesn't have voltage when trying to reset the breaker: yes, we did that. I had someone disconnect the shunt wires completely, and it still wouldn't reset.
Here is what I'm going to do: I'm going to ask the supplier nicely if they'll cover a replacement, and if not I'll buy a new one. The issue of fault current only came up because I was thinking I might buy a lower-rated one to save money. But I prefer to keep the panels fully rated to 22k as they are now, instead of installing one lower-rated breaker.