New spa need info please.

Status
Not open for further replies.

butch

Member
I am in the process of hooking a new electric service a spa ,the disconnect on the wall located 9 feet away has a 2 pole 20amp gfci breaker and a 30 amp 2 pole gfci breaker, I tryed to call the technicians yesterday but they will be open today in the master unit in the spa it has 5 places for terminations it shows the 20 amp gfci breaker just to be connected to the neutral bar on the 30 gfci brk it shows the white wire to run to the spa the terminal to the terminal board . Can any one help me in explaining the reason for 2 breakers running to the spa?
 
Re: New spa need info please.

Butch,

I don't know if this is simialr to your situation, but I've seen Spas (years ago) which were fed with two different circuits. They had a 20A 120v circuit for the Pump and control circuits, etc. and a 30A 240v that was strictly for the heater.

Bill
 
Re: New spa need info please.

Thank You SO Much Gentlrmen for your replys, but the home homeis saying tis configuratuion with 2 Brekers has only benn out for appx 1 month or a little longer Im going to talk to the service tech and get some furater info, again thank you both for you reply.
 