Never used a 60Hz TDR, but....
A while back, I spent time pondering this topic. And have a question to add to the muddle.
What happens if the load reactor is mounted at the motor,
X hundred feet from the VFD?
Discuss.
The "spike" issue is the result of the fast rise time of the leading edge (dV/dt) of the PWM DC pulses causing the conductors to act like capacitors, and a charge builds up between them. That charge gets reflected back and forth between the drive and the motor until it builds to the point where its potential exceeds the insulation rating on the magnet wire in the windings or the cable insulation, sometimes both. Putting a reactor at the drive adds an inductive time constant to the PWM pulse current, because in an inductive circuit, the current through it cannot change instantaneously. That then also slows the voltage rise time as well, reducing (not eliminating) the cause of the reflected wave phenomenon. Putting the reactor at the load end can allow the reactor to absorb those voltage spikes before they reach the motor insulation, but do nothing to protect the cable.
Using the shielded cable (as Besoeker does and as do most people in the EU because it is required) significantly reduces that cable capacitance issue, that's why he rarely sees problems. In this country, THHN gets pulled for motor leads because that's the way it was always done (hopefully in steel conduit), but that does nothing to reduce that capacitance issue.
The most common reasons why people often say "I've never had a problem" are:
1) most of the drives they have done are 208-230V. The issue exists, it's just that the spikes don't exceed the insulation rating.
2) they have been using older drives that still used darlington transistors, which have a much slower turn-on time, so the leading edge of the PWM pulses is not as steep.
3) they have been using newer IIGBT based drives, but ones that employ specific circuit design techniques to reduce the capacitance and thus increase the acceptable drive-to-motor distance. Case in point, many AB PowerFlex drives list the TESTED drive-to-motor distance as being hundreds of feet, with no load reactors, filters, or shielded cable. Adding any of those extends that distance even further, but at that point, voltage drop becomes problematic too so people tend to keep the distance short anyway.
4) they are always dealing with short distances, as in under 50ft.