ggunn
- Austin, TX, USA
- Consulting Electrical Engineer - Photovoltaic Systems
The three phase resultant is exactly the second result, 72.9A.
That would be appropriate for feeder and OCPD determination, and should be the same number you get using the power formula.
There is no question, IMHO, about how the NEC says to do that calculation in the case of actual loads.
But for sources, the specific language seems to rule out doing it the same way. If 690 had you add the power and then determine the current, it would give your result. But it seems to require "adding" the currents instead without saying just how that should be done.
(21000)(1.25)/(208)(sqrt 3) = 72.86. 80A breaker. (There is no 75A IIRC, but my code book is at work.)
Good. That's how I have been doing it.