NFPA 110 Ch. 7.2.3

anbm

Senior Member
Location
TX
Occupation
Designer
Per above code, level 1 EPSS (emergency power supply sytem) equipment can not be located in same room with the normal service equipment if service equipment >150V to ground and >= 1000A. Can someone give me example of level 1 EPSS equipment? I assume this includes main emergency generator distribution panel, emergency ATS (serving egress lights, fire alarm, life-safety equipment, etc.), will the first panel downstream of emergency ATS counts as well or just the emergency ATS?
 
Since an EPSS Level 1 requires a 10 second power supply availability, so that would be a NEC 700 load which is identified in the adopted building code Chapter 27 with loads labeled as "Emergency"
 
Since an EPSS Level 1 requires a 10 second power supply availability, so that would be a NEC 700 load which is identified in the adopted building code Chapter 27 with loads labeled as "Emergency"
Which equipment will be considered EPSS equipment? Try to figure out the boundary...
 
Top