The problem is after they fail this I'm going to have to fix it.. the customers already said that if the inspector doesn't like it she'll have me spin the panels around to face the room on the other side...

Sent from my Nexus 6P using Tapatalk

No problem, more money more money!
 
Here is commentary from the NECH and yes, I know the commentary isn't code but in this case it's accurate.

(2) Width of Working Space. The width of the working spacein front of the electrical equipment shall be the width of the
equipment or 762 mm (30 in.), whichever is greater. In all
cases, the work space shall permit at least a 90 degree opening
of equipment doors or hinged panels.
Regardless of the width of the electrical equipment, the working
space cannot be less than 30 inches wide as required by
Table 110.26(A)(1). This space allows an individual to have at least
shoulder-width space in front of the equipment. The 30-inch measurement
can be made from either the left or the right edge of the
equipment and can overlap other electrical equipment, provided
the other equipment does not extend beyond the clearance
required by Table 110.26(A)(1). If the equipment is wider than
30 inches, the left-to-right space must be equal to the width of the
equipment. Exhibit 110.15 illustrates the 30-inch width
requirement.
Sufficient depth in the working space is also required to
allow a panel or a door to open at least 90 degrees. If doors or
hinged panels are wider than 3 feet, more than a 3-foot deep
working space must be provided to allow a full 90-degree opening.
(See Exhibit 110.16.)



Roger
 
Something you may want to check on; did the owner hire their Brother-in-Law to do the plumbing, and did he "piggyback" onto YOUR permit? That could end up looking like you were the contractor for the plumbing too. I've seen that happen in the past, although MOST places have safeguards against that now.
Where I am the customer gets a building permit which allows all the different trades to start work. Then I have to file for a rough electrical inspection. There's no electrical permit to start working. This is why in my area it's very common to see an unlicensed person start a job then the customer calls in a licensed electrician to get an inspection and finish... They'll just say something like I kicked the last contractor off the job and he closed up shop and was never heard from again but really it was their cousin who's a mechanic for somebody else.

Sent from my Nexus 6P using Tapatalk
 
Where I am the customer gets a building permit which allows all the different trades to start work. Then I have to file for a rough electrical inspection. There's no electrical permit to start working. This is why in my area it's very common to see an unlicensed person start a job then the customer calls in a licensed electrician to get an inspection and finish... They'll just say something like I kicked the last contractor off the job and he closed up shop and was never heard from again but really it was their cousin who's a mechanic for somebody else.

Sent from my Nexus 6P using Tapatalk
Or guys will do a job and then just get a licensed contractor to file for an inspection for them

Sent from my Nexus 6P using Tapatalk
 
Or guys will do a job and then just get a licensed contractor to file for an inspection for them

Sent from my Nexus 6P using Tapatalk
It's really messed up but also the the licensing where I am is ridiculous... There's two counties and then multiple municipalities within each County. So within a 50-mile radius there's 5 licenses you would need

Sent from my Nexus 6P using Tapatalk
 
It's really messed up but also the the licensing where I am is ridiculous... There's two counties and then multiple municipalities within each County. So within a 50-mile radius there's 5 licenses you would need

Sent from my Nexus 6P using Tapatalk

Makes NJ seem reasonable, and that's saying a lot.
 
It's really messed up but also the the licensing where I am is ridiculous... There's two counties and then multiple municipalities within each County. So within a 50-mile radius there's 5 licenses you would need

Sent from my Nexus 6P using Tapatalk

Hartford County, MD? :lol:

Lovely pics... that mudring outside the wall isnt as bad as the drywall screws attaching it to...I presume a box. Also, spin the panels around? :jawdrop: I dont think I've ever seen a panel that had enough slack in the wiring to allow that... let alone if there is any conduits going to it.

Maybe I need to start installing service loops at the panel to plan for such things.... NOT!
 
The problem is after they fail this I'm going to have to fix it.. the customers already said that if the inspector doesn't like it she'll have me spin the panels around to face the room on the other side...

Sent from my Nexus 6P using Tapatalk
Does she think you may be wrong and that it may pass? Not that some places it might, but if you regularly work in that area one has to assume if you say it won't pass that you are most likely correct.

If that were to happen to me around here - there is not only the requirement to fix the violations, but also a reinspection fee. Costs less to do it right the first time. Now if they sneak that sink in there on me after rough in and client wants to wait for it to fail before authorizing me to change it - I may explain the situation to the inspector, he may even come out and tell owner personally he will not pass that, and there won't be any additional charges from inspection dept. But if I wait until final inspection day to let him see it - there will be a correction notice and reinspection fees.
 
Does she think you may be wrong and that it may pass? Not that some places it might, but if you regularly work in that area one has to assume if you say it won't pass that you are most likely correct.

If that were to happen to me around here - there is not only the requirement to fix the violations, but also a reinspection fee. Costs less to do it right the first time. Now if they sneak that sink in there on me after rough in and client wants to wait for it to fail before authorizing me to change it - I may explain the situation to the inspector, he may even come out and tell owner personally he will not pass that, and there won't be any additional charges from inspection dept. But if I wait until final inspection day to let him see it - there will be a correction notice and reinspection fees.
They snuck it in after rough inspection.. To be honest the inspectors around here don't look at much when I got my rough inspection the guy came in and asked me for counts then asked me if I used anti short bushings on all the mc cable and opened up one box to see and then left. He was there for 5 Minutes

Sent from my Nexus 6P using Tapatalk
 
They snuck it in after rough inspection.. To be honest the inspectors around here don't look at much when I got my rough inspection the guy came in and asked me for counts then asked me if I used anti short bushings on all the mc cable and opened up one box to see and then left. He was there for 5 Minutes

Sent from my Nexus 6P using Tapatalk
So she thinks the inspector won't even notice which is probably true

Sent from my Nexus 6P using Tapatalk
 
Some inspectors here may not have mentioned anything about the pipes if they would have been there at rough inspection, but none of them would give a go on a final if that sink were in front of the panel. That is why I said if it happened to me I wouldn't be waiting to see if it is overlooked - it won't be around here. They can even go through things kind of fast and miss some minor things at times, but they always look at panelboards. For one thing the electrical permits here are somewhat based on number of branch circuits that were installed/worked on. On new construction they will count breaker handles to verify you filed for the correct number of circuits. On existing is not always so clear as they need to determine what is new and what was existing.

If that sink were already in front of the panel before you had done any work (if you were working here) they will still do what they can to try to get things changed, but you wouldn't necessarily be as directly responsible for making sure it gets changed - especially if you didn't add any circuits to that particular panel, if you did add circuits to that panel then you will likely not get out of making changes before they finalize your permit.
 
So, the sink is not a problem considering it can be modified to not protrude pass the edge of the panel, what is the actual measurement to the edge of the washer going to be?

Roger
 
To be honest the inspectors around here don't look at much ..asked me if I used anti short bushings on all the mc cable and opened up one box to see and then left. He was there for 5 Minutes

If your connectors were listed for MC Cable, anti-short bushings are not supposed to be needed.

So, the only thing inspector looks for was not required. Bet you keep using red devils on your MC.
 
So, the sink is not a problem considering it can be modified to not protrude pass the edge of the panel, what is the actual measurement to the edge of the washer going to be?:thumbsup:

Roger

Roger is asking once the washer is placed will you have 36" in front of panel...does not look good.
 
Roger is asking once the washer is placed will you have 36" in front of panel...does not look good.

OP said the washer will be at far left (i.e beyond the drain pipe.) It appears to me that the distance from the panel front to the drain pipe is more than 36", but it is hard to tell for sure from a photo without making some geometric calculations and knowing some optical information about the camera and its position.
 
OP said the washer will be at far left (i.e beyond the drain pipe.) It appears to me that the distance from the panel front to the drain pipe is more than 36"
That is the way it appears to me too.

Roger
 