Sections 358.30(A), 358.30(B)
(A) Securely Fastened.
EMT shall be securely fastened in place in accordance with the following:
Exception No. 2: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable, unbroken lengths (without coupling) of EMT shall be permitted to be fished.
(B) Supports.
Horizontal runs of EMT supported by openings through framing members at intervals not greater than 3 m (10 ft) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
(C) Conduit sections 24" or less are considered to be "nipples" and can be unsupported for lengths of 24" or less.
Do you think 358.30(C) should be added back to the 2026 code cycle?
(A) Securely Fastened.
EMT shall be securely fastened in place in accordance with the following:
- At intervals not to exceed 3 m (10 ft)
- Within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other tubing termination
Exception No. 2: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable, unbroken lengths (without coupling) of EMT shall be permitted to be fished.
(B) Supports.
Horizontal runs of EMT supported by openings through framing members at intervals not greater than 3 m (10 ft) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
(C) Conduit sections 24" or less are considered to be "nipples" and can be unsupported for lengths of 24" or less.
Do you think 358.30(C) should be added back to the 2026 code cycle?