Why is that?That would not be required if you have industrial experience.
Why is that?That would not be required if you have industrial experience.
I understand...That is what I was doing with the proposed exception, but I was going to restore the original proposal which was fro 36", not the 18" that the CMP modified it to.I am attempting to add 358.30(C) back with 24" instead of 18"
It’s been long enough since the 2008 proposal, there are new CMP members ( including Ryan Jackson), so make the proposal, er, public comment.I am attempting to add 358.30(C) back with 24" instead of 18"
Offsets on larger raceways are seldomly needed to incorporate supporting hardware.Why is that?
Ryan is not on CMP-8 but I see your point that is my only proposal I have even the slightest hopes pass my other proposals are a deliberate attempt to add clarity to some unclear situations that have no real world implications or merit.It’s been long enough since the 2008 proposal, there are new CMP members ( including Ryan Jackson), so make the proposal, er, public comment.
The language "within" 36" would make that a difficult situation must be securely fastened within 36" unless the exception applies then it's not required LOLI understand...That is what I was doing with the proposed exception, but I was going to restore the original proposal which was fro 36", not the 18" that the CMP modified it to.
There isn't any it was an answer to your question.Can you post that reference? I am not aware of that specific wording
Oh I agree thenThere isn't any it was an answer to your question.
The exception in my proposal said that the conduit termination shall be permitted to be used for the required securing and supporting of an unbroken straight raceway of 36" or less (ore something like that, been a few years and not going to go back and look it up)...,much like the cable termination fitting is permitted to secure and support a fixture whip.The language "within" 36" would make that a difficult situation must be securely fastened within 36" unless the exception applies then it's not required LOL
Other sections of the NEC make that a tough sell such as 410.36(E) I feel 24" unsupported reference could apply to solid raceways across the board.The exception in my proposal said that the conduit termination shall be permitted to be used for the required securing and supporting of an unbroken straight raceway of 36" or less (ore something like that, been a few years and not going to go back and look it up)...,much like the cable termination fitting is permitted to secure and support a fixture whip.
Then how does 24" work when 314.23(E) & (F) specify 18"?Other sections of the NEC make that a tough sell such as 410.36(E) I feel 24" unsupported reference could apply to solid raceways across the board.
I don't think any PI to says lengths less than x" do not need support will pass unless the unbroken and straight language is there. I agree that it is not needed, but ...Seems most logical, simple, and reasonable to just follow the same support rules for a given raceway and just clarify a termination can be the support when the distance to it is less than or equal to the max support distance. Sounds like that's pretty much what Don proposed, although I don't see why it would have to be unbroken. We can put together a bunch of small pieces with couplings on EMT and still have the first support at 3 ft, so why should it be any different between cabinets? Just seems like an incredible amount of hand wringing going on over this and it just seems so simple to me.
How does it work currently saying nothing?Then how does 24" work when 314.23(E) & (F) specify 18"?
Very well as very few AHJs enforce what the current rule actually says. In many cases they do exactly what my PI would have put into the code, that is where the raceway is 3' or less, they permit the opposite end conduit support to be the required securing and supporting within 3'.How does it work currently saying nothing?
I will be very interested to see what the substantiation is for all my public inputs to be rejected. I feel the overall exception for 210.8 is really good.Very well as very few AHJs enforce what the current rule actually says. In many cases they do exactly what my PI would have put into the code, that is where the raceway is 3' or less, they permit the opposite end conduit support to be the required securing and supporting within 3'.
Of course this makes perfect sense but the CMP responsible for this rule is really dumb so we can just bang our heads against the wall because you can't fix stupid.Count the connector as the support it is, and does provide. Every run of raceway needs 2 supports. A connector terminated in a solidly mounted enclosure, box or fixture is counted as a support. for a raceway shorter than the minimum unsupported length shall be considered supported where the connector meets the 1st requirement.