Hi All,
I wanted to verify that an N2O Storage tank is in a classified 1 div 1 location according to the NEC 515.3 and Table 515.3 (Tank- Aboveground). Thus the stated area will require fittings and wiring methods per 501 or 505 depending on the classification method used?
This N2O tank is also with in 6ft of a CO2 storage tank. Are there any other methods or practices I may want to consider?
There are drawings of this project, but they are basically a site plan with equipment locations. Nothing about explosion proof fittings or the area being classified. The AHJ has not issued the permit and I can only assume they will be asking for these classifications to be included. So I wanted to get a jump on this and be as prepared as possible.
Thanks...
I wanted to verify that an N2O Storage tank is in a classified 1 div 1 location according to the NEC 515.3 and Table 515.3 (Tank- Aboveground). Thus the stated area will require fittings and wiring methods per 501 or 505 depending on the classification method used?
This N2O tank is also with in 6ft of a CO2 storage tank. Are there any other methods or practices I may want to consider?
There are drawings of this project, but they are basically a site plan with equipment locations. Nothing about explosion proof fittings or the area being classified. The AHJ has not issued the permit and I can only assume they will be asking for these classifications to be included. So I wanted to get a jump on this and be as prepared as possible.