Not to offend or disrespect but what's with the 1 or 2 word or numbers answers, which I have seen a lot of, can't we just give the code referance like for instance NEC 2005 334.15 (B) and go on, the man is asking for advice .By Ryan: 2002 or 2005?
Theres not. The prohibition in 2002 was a mistake and lack of communication between CMP's 7 and 8. I spoke with Gaylen Rogers (chairperson of panel 7) about this is a few years back during the ROC of the 2005.Originally posted by peter d:
I am still at a loss to understand the safety hazard of running NM cable inside of a raceway in a dry location.
I stand corrected Sir, that is why you are the inspector, and from what I have seen of your posts you sure know your stuff, I guess I need to open my code book more often. I'm still under the 2002 but on this one I will have to disagree and quote NEC 2002 344.15(B)Because there was a code change that addressed this. I need to know which code applies before I answer.
Under the 2002, I would refer you to 358.22 and tell you it is a violation.
Under the 2005, I would refer you to 358.22 and tell you it is not a violation.
Originally posted by ryan_618:
The question then becomes...how long of a peice of EMT can you use? I would have no problem signing off on a ten foot length, but I would have issues (under the 2002) with anything more. Again, it really isn't a safety issue, and once I learned that this was simply a mistake I would have allowed more than 10'.
I do think, however, that an inspector would be justified in writing this as a violation in the 2002, however silly that may be.
In my opinion, if both ends of the conduit are attached to boxes, etc., with connectors, it's a conduit system; otherwise, it's a sleeve.Originally posted by ryan_618:
When is the line crossed between a sleeve and raceway?
Conduit stub: to me says it is an open ended piece of conduit (sleeve)Originally posted by automaton:
indoors from a basement to a conduit stub leading to a 10' piece of conduit up to an outdoor fixture?
Yes I do.Originally posted by macmikeman:
Don't you think its sorta dumb .......