This type of romex installation, although commonly done is not CODE compliant because 314.17(B) says,in part: "Where raceway or cable is installed with metal boxes or conduit bodies, the raceway or cable shall be secured to such boxes or conduit bodies."
This requires that the type NM cable be secured to the box, which is not possible because the cable is enclosed in EMT and there is no way to install an approved box connector on it.
There are only 2 places in the CODE where type NM cable can be connected to an enclosure without the use of a cable connector.
The 1st is the exception to 314.17(C) where type NM can enter a single gang nonmetallic box if the cable is supported within 8 inches of the box and the sheath extends into the box at least a 1/4 inch.
The 2nd would be the exception to 312.5(C) where a group of NM sheathed cables are permitted to enter the top or an enclosure through a raceway between 18 inches and 10 feet in length provided:
1)The cable sheath extends at least a 1/4 inch beyond the lower end of the raceway.
2)The raceway is properly supported.
3)The cables are fastened not more than 12 inches beyond the upper end of the raceway.
4)Conduit fill requirements are followed.
5)Fittings to protect the cable from abrasion are installed on both ends of the raceway.
6)The raceway is sealed to keep vermin and debris from entering the raceway.
7)Derating factors are applied.
The limitations of 312.5(C) give guidance to the allowable length of raceway used to protect type NM cable from damage.Therefore it is reasonable to say that the limit for the length of raceway used for physical protection of NM is 10 feet.If the need for protection exceeds 10 feet, a splice box should be inserted between the cable and the raceway, and a change in wiring methods must be made, as required by 300.15
shortcircuit2