shboal11
Member
- Location
- Grand Terrace, California
I was over ridden the other day on a call, need to know if I missed anything. (17) 12-2 nm cables in a 6ft long 2in PVC conduit, the cables sheath was removed prior to installation. 2 of the circuits serve kitchen small appliances.
my call wire ampacity based on 310.15 (B)(16) 30 amps. Wire ampacity to be reduced 50% 310.15 (B)(3)(A) 15 amps. Small appliance min amperage is 20 amps 210.52(B)(1). marking on wire required 310.120(B)(1).
my call wire ampacity based on 310.15 (B)(16) 30 amps. Wire ampacity to be reduced 50% 310.15 (B)(3)(A) 15 amps. Small appliance min amperage is 20 amps 210.52(B)(1). marking on wire required 310.120(B)(1).