For derating you can use 90 deg, see 334.80#12 NM is not rated for 30 amps.
Roger
How about the marking requirements in 310.120?Please cite the code section you believe requires that.
110.3 (B)....Please cite the code section you believe requires that.
Also keeping in mind that all manufacturers of NM-B do not mark our inner conductors because UL 719 permits this.
So you cannot tell at the junction box or transition the conductors in the conduit are the same conductors of the cable assembly. :lol:How about the marking requirements in 310.120?
Most if not all NM cable has no markings on individual conductors, once you strip the sheath off you are left with a conductor that doesn't comply with 310.120 at the very least, if left within the sheath, the sheath is marked to comply with 310.120.
Who is yall....they made it long before I came. But I will tell you as for the sheathing it's the same PVC...just with less additives needed for insulation since NM-B location use is limited....about all I can tell you without special handshakes and security clearances.
The insulation itself on the wire are exactly equivalent to THHN without the markings or nylon covering . However, nothing prevents us from using normal THHN with markings...but why...ink is expensive.
Comments based on the 2017 National Electrical Code.
I can understand that....Agreed. But now they know...lol...or they could just read UL 719 and really know...lol.I was poking fun at all the people that claim to know what the insulation is. Not actually directed at you.
Some say THHN and some say THWN, some swear they know.
I say who cares. The NEC says it is simply a 90C conductor limited to 60C for final ampacity. That works for me.
I can, NEC says I can'tSo you cannot tell at the junction box or transition the conductors in the conduit are the same conductors of the cable assembly. :lol:
Where? :huh:I can, NEC says I can't![]()
310.120 Marking.
(A) Required Information. All conductors and cables
shall be marked to indicate the following information, using
the applicable method described in 310.120(B):
(1) The maximum rated voltage.
(2) The proper type letter or letters for the type of wire or
cable as specified elsewhere in this Code.
(3) The manufacturer's name, trademark, or other distinctive
marking by which the organization responsible for
the product can be readily identified.
(4) The AWG size or circular mil area.
Informational Note: See Conductor Properties, Table 8 of
Chapter 9, for conductor area expressed in SI units for
conductor sizes specified in AWG or circular mil area.
(S) Cable assemblies where the neutral conductor is
smaller than the ungrounded conductors shall be so
marked
Second issue, if in fact that section means what many feel it means where is the permission to remove that marking when entering an enclosure?
You mean this 310.120?
The 310.120 found in Part III Construction Specifications of article 310?
First issue I have with that is I do not construct wire and cable, I install it. That section is aimed at manufacturers not the end user.
right it is construction requirements. Stripping sheath off and pulling the remaining conductors is de-constructing something that originally met the construction requirements.
Isn't it kinda implied that we can remove the sheath with that "the sheath shall extend at least 1/4" into the box/enclosure" rule?
I'd say I was partly kidding yet partly serious.You are kidding me now right?
Because you cannot possibly be serious with that response. :huh:
:thumbsup:I'd say I was partly kidding yet partly serious.
Strip the sheath off and what are you left with to be able to identify the conductors as something acceptable for use by NEC? Right after you remove conductors from sheath you knew what they come from. Bring in a third party that had nothing to do with the install and how do they know if it is THHN, THWN, TFFN, MTW, etc. or if it is even a conductor permitted by NEC.
Out of all the thousands, if not millions of miles of wires I've pulled and terminated, do you know how many I've checked the type of wire after pulling it?:thumbsup:
Whereas if you strip the sheath at the boundary of a box, leaving even a bit inside, it should be clear what the conductors are part of.
:thumbsup: