The 1/4" of sheath serves no purpose for identification.
Just physical protection at that point.
The 1/4" of sheath serves no purpose for identification.
Nm cable can only have the sheath removed in the J box. With out the sheath it would not have any markings, therefore a code violation. The conduit is acutely EMT installed on the side of the house in Wrightwood. Snow area
Sent from my SM-G930V using Tapatalk
That's right for the typical case.The 1/4" of sheath serves no purpose for identification.
... using some of the sheath to identify the conductors would fix that problem...
That's right for the typical case.
I was referring to a common objection to using unsheathed NM conductors in a raceway after a proper transition from open NM cable, namely that the individual conductors in the NM cable are not labeled. Not sure if that is really a code violation, but if it is I believe using some of the sheath to identify the conductors would fix that problem.
Cheers, Wayne
That may be true. In the case I an referring to is about 8 ft long. Now in your case the sheath must be on the cable no matter what the length is, if it is exiting a junction box and not in a chase.Depending on what part of the cable your looking at, your not going to get a lot of information off of it anyway.
So if I install a short piece of NM that doesn't have the markings on it between 2 boxes, is that a violation?
NOT.
JAP>
It wouldn't. You could use a long enough section of sheath to include the identifying information printed the sheath.How would a small piece of sheath ever identify the conductors?
...as far as I can tell, the requirement for 1/4" of NM cable sheath to extend into a box applies only to non-metallic boxes and conduit bodies (314.17(C)) and a few other specific allowances...
It wouldn't. You could use a long enough section of sheath to include the identifying information printed the sheath.
Though I am on the side that says the sheath must be on the cable within the pipe, I think by using a piece of NM sheath he is trying to identify which conductors are part of same cable as well as indicate they are NM cable.How would a small piece of sheath ever identify the conductors?
As far as I know, the sheath on NM whether it be, orange, yellow or white is mostly all the same stuff.
If I happened to use a piece of orange sheathing laying around to satisfy the rule of having to have a 1/4" of sheathing inside of the enclosure, and the stripped cable in the conduit happened to be #12 or 14 instead of #10, would my problem still be fixed?
No.
JAP>
I was over ridden the other day on a call, need to know if I missed anything. (17) 12-2 nm cables in a 6ft long 2in PVC conduit, the cables sheath was removed prior to installation. 2 of the circuits serve kitchen small appliances.
my call wire ampacity based on 310.15 (B)(16) 30 amps. Wire ampacity to be reduced 50% 310.15 (B)(3)(A) 15 amps. Small appliance min amperage is 20 amps 210.52(B)(1). marking on wire required 310.120(B)(1).