Maybe it was installed by the same guy who did this:
![]()
What in the world
Maybe it was installed by the same guy who did this:
![]()
Maybe it was installed by the same guy who did this:
![]()
Let me guess. The "PULL-THOUGH BOX COUPLING" for the lack of a better term to describe this unique installation, was in an un-accessible location.
That's my guess. It was originally run in a space that was going to be accessible. (or so the installer thought) After he found out he screwed-up, he had to make it pass through?!?Who knows? Somebody went through an awful lot of trouble to make this rig! Notice the EMT connectors inside the box are cast and the originals are steel. Is that a Rigid coupling cut in half? It does serve as a VERY fancy EMT strap!
![]()
I also dont know the exact cu." but the the two conductors count as one each and the ground would not count, well only one would so it should be ok as is for box fill. What I am trying to say is I dont see any violation, but would be interesting to find out for sure.
How would the example be any different than Exhibit 314.1 Handbook?
Grounds count as 1
I don't think anything in the code says that...in order for a ground wire to be considered an EGC it must be connected to all EGC's in the box and to the equipment.
The ground wire inside the NM is not an EGC and must be counted seperatly.
I understand we say " All grounds count as one", however what we mean is All Equipment Grounding Conductors Count as one.
Do you see my point.???
Take a look at this example with a separate ground wire. According to 314.16(B)(5), we count them separately.
Any thoughts???
314.16 (B)(1)
(B) Box Fill Calculations. The volumes in paragraphs
(1) Conductor Fill. Each conductor that originates outside
the box and terminates or is spliced within the box shall be
counted once, and
each conductor that passes through the
box without splice or termination shall be counted once
So you would count the EGC that passes through the box per this NEC section.
Each conductor that originates outside
the box and terminates or is spliced within the box shall be
counted once, and each conductor that passes through the
box without splice or termination shall be counted once.
When I read this I don't see where it designates the use of the conductor i.e. grounded, undgrounded, grounding.
I definitly see where there can be a case made for both, I think I would erre on the side of either putting in a larger box so as not to have to change it later, or checking with the AHJ.
If there is a definitive code reference I would like to know..
Take a look at this example with a separate ground wire. According to 314.16(B)(5), we count them separately.
Any thoughts???
I think it would be a stretch to say that the equipment ground in the continuous NM in the opening post is there to provide an isolated ground.
I don't think anything in the code says that
The ground in the continuous NM is still an equipment ground even though it isn't grounding equipment at this box. It would presumably ground equipment somewhere else.