hurk27
- Portage, Indiana NEC: 2008
Re: NM cable thru studs
First I have run into this problem too. And when I tell the AHJ that we are allowed to use table 310.16 to derate from he acts surprised. and with 310.16 a #14 is allowed 25 amps to start with and would take a 60% derating to get to the 15 amps that we are required to protect the circuit with anyway so this alone will allow 9 current carrying conductors "bundled" But I don't believe, that if you can keep the runs loose enough to separate them after each stud or joist it is bundled. Otherwise the floor joist or wall studs would look like swiss cheese.