bjp_ne_elec said:
312.5(C) Exception - doesn't this allow the NM not to be secured to the enclosure as one of the expceptions?
Yes. But when we are handed ten provisions in that exception (three are concealed in the opening sentence), all of which must be observed to use the exception, I would call that a "tall" exception to the rule.
I'm also interested in hearing how you secure cables to enclosures, etc.
Personally, I recess panels, and install plastic romex connectors.
If I have to surface mount a panel, then I install a running board and secure the romex within 12" of the panel, and use romex connectors.
And again - does anyone out there have a photo that would help clear my understanding of what the Exception to 312.5(C) is all about.
I don't have a photo, but I can give you a verbal, maybe that might help?
I use a ram-set to mount an indoor panel to the wall of a basement. I now have to run the cables into the panel, but my jurisdiction (say, San Francisco) does not allow romex under 8' to be exposed at all, it must be sleeved in a conduit. This presents me with a problem, because (the main rule of) 312.5(C) says that the cables must be secured to (clamped to) the enclosure.
I'd like to use a 2" or 2.5" EMT right up the wall.
I'm in luck: as long as I adhere carefully to the exception, I can skip securing the cables to the enclosure.