Re: NM Raceway?
I doubt highly that the listing is "Listed for supporting NM out in the open of unfinished basements"
[ May 30, 2004, 08:15 AM: Message edited by: iwire ]
That is my feeling too, even if we accept that these are listed NM hangers we must use them in a code compliant manner.Originally posted by pierre:
These 'hangers' (which in my estimation are low voltage roughing plates) will not satisfy the requirement, therefore are not compliant.
I do not agree, no matter what the listing of these units are they must be used in a code compliant manner. How would you use these and meet the requirements of 334.15Originally posted by msd:
What is this product, and is it listed for this application? That is all that matters.
Someone please explain to me how a listed product can change the above requirements?334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface. The cable shall closely follow the surface of the building finish or of running boards.
(C) In Unfinished Basements. Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards.
I doubt highly that the listing is "Listed for supporting NM out in the open of unfinished basements"
[ May 30, 2004, 08:15 AM: Message edited by: iwire ]