The cable fill chart is part of the listing, we also have a calculation chart to calculate for combinations of cables. The 40% was something that I wanted due to heat dissipation.
An example of one of the temperature test:
38-14/2 NM cables (40%)installed in the system with
12 amps on every conductor.(80% of overcurrent device) 912 amps flowing through the system without over heating the conductors or the product.
The verbiage has been changed to state that it was tested to 80% of the overcurrent device.