As long as where dealing with resistance only and single phase or rise and fall happen same time across the windings DC or AC shouldn't matter.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
ronaldrc said:
As long as where dealing with resistance only and single phase or rise and fall happen same time across the windings DC or AC shouldn't matter.
That was my point: splitting the neutral for separate DC meters won't change anything relative to a single AC meter.
]Larry I don't have any in line ammeters.
Not even in your voltmeter?
 

ronaldrc

Senior Member
Location
Tennessee
Larry

Its worth a try if it does flow we will have to rethink harmonics.

Heres what I thought about after I posted that last night.


I have not run this experiment yet.So I don't know yet rather current actually flows or not with a balanced circuit.

The example I am showing is indicating or showing that there is actual current flowing on the neutral.The two meters with the diodes
on both sides prevents the meter from getting current from both directions so they read 10 amps. The one single top meter gets an equal amount of current flow from both sides so it will read null or zero.


If current does flow which I don't think it does,then we will have to go back rethink our theory on why the neutral conductor gets hot even when it shows no load with the standard clamp on ampere Meter.


Ronald :)
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
ronaldrc said:
If current does flow which I don't think it does,then we will have to go back rethink our theory on why the neutral conductor gets hot even when it shows no load with the standard clamp on ampere Meter.[/b]

I think that I missed something.

Do you have a real situation where you have a neutral that is getting hot, but are measuring no current flow on it?

-Jon
 

ronaldrc

Senior Member
Location
Tennessee
winnie said:
I think that I missed something.

Do you have a real situation where you have a neutral that is getting hot, but are measuring no current flow on it?

-Jon


Hello Jon

No but I have read articles about it when discussing Harmonics.

I don't think this is the case I was just thinking out of the box,I probably shouldn't have mentioned it. :)
 

ELA

Senior Member
Occupation
Electrical Test Engineer
Plumbing Analogy helpful?

Plumbing Analogy helpful?

Anybody think the fluid flows in the common return in both directions at the same time?

BalancedPumpFlo.jpg


I vote for zero differential pressure drop across the return line and thus very little flow.
 

rattus

Senior Member
Experiment:

Experiment:

Ronald,

The reason that you cannot prove or disprove this with an experiment is that nothing is happening; there is nothing to measure.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
ronaldrc said:
If current does flow which I don't think it does,then we will have to go back rethink our theory on why the neutral conductor gets hot even when it shows no load with the standard clamp on ampere Meter.
Where have you ever seen this phenomenon? I believe it to be impossible, and that harmonic current would be read.
 

ronaldrc

Senior Member
Location
Tennessee
Rattus

That was my real belief that there was no current flow but its always been in the back of my mind maybe thats not the case. I'm more guilty than anybody to say if it looks like a Duck and quacks like a Duck its a Duck.

Larry

I read a article once not to long ago where a neutral was running warm and it did not read any current with a regular clamp on ammeter. I did a search in meters and harmonics and couldn't find anything.

Threads are cheap I give fair warning and it was fun. :)

Larry I like the cat video
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
ronaldrc said:
Rattus

Threads are cheap

Well Ronald, just think, we could have worked a buss extension into the thread for a little bit more. :grin:

Roger
 

ronaldrc

Senior Member
Location
Tennessee
Benaround

I know this whole idea I have seems like a childest question but I have always had to see something in a practical demostration to understand it.

But even my DC circuit does not work since the positive flow would flow through the diodes to toward the bottom and meet somewhere in the junction of diode #2 and oppose each other and at that point stop dead in there tracks.

Winnies idea about the heat being generated in the neutral is proof enough that know current flows.

Larry I was not putting you on.

I know I read some litature that a neutral would run warm and a standard non rms clamp on ammeter would not read the current because it was harmonics. Thats what give me the idea that there might be current flow on a balanced neutral altough I always believed there was not. :)
 