Can i run a single #12 thhn green to each outlet for the egc ?
You can, tho why would you want to?
Less work than a total rewire, easier to snake into the box than a new cable would be my guesses.
Totally disagree, it's just as easy to use that #12 to pull some romex into the box. You have to run that ground wire back to the panel to do it correctly anyways. Just rewire... do the right thing. You're creating awkward hazardous situations for homeowners and future electricians if you just run a ground. Romex is cheapLess work than a total rewire, easier to snake into the box than a new cable would be my guesses.
Totally disagree, it's just as easy to use that #12 to pull some romex into the box. You have to run that ground wire back to the panel to do it correctly anyways. Just rewire... do the right thing. You're creating awkward hazardous situations for homeowners and future electricians if you just run a ground. Romex is cheap
Sent from my SM-G950U using Tapatalk
Totally disagree, it's just as easy to use that #12 to pull some romex into the box. You have to run that ground wire back to the panel to do it correctly anyways. Just rewire... do the right thing. You're creating awkward hazardous situations for homeowners and future electricians if you just run a ground. Romex is cheap
If the house is from the 50's you're going to have a hard time finding a ground anywhere other than the panel. 9 out of 10 times that useful ground in the jbox will also have hot and neutral you can use.too tired to get out codebook
but although we are no longer allowed to run to nearby water pipe, we don't always have to run green all the way back to panel, nearest receptacle or junction box
with large enough ground is still allowed
As to why run just a green when just as easy to run new romex:
Sometimes customer only needs a few receptacles grounded, often on several different circuits
And sometimes grounding existing overhead light fixtures is not practical, but circuits are run spiderweb from light fixture box
I'd rather do complete $12k rewire, but sometimes budget is more like $1.2k
The labor should be about the same unless you're running the wire like the cable guy.I fail to see how adding a ground is creating "awkward hazardous situations". It's the exact opposite, adding a ground is greatly improving safety.
Romex actually isn't that cheap anymore. But what's really expensive is the labor to install it.
Less work than a total rewire, easier to snake into the box than a new cable would be my guesses.
Isn't the 12-2 a 250ft roll?12/2 is $75, a 500ft roll of #12 is $55.
Im staying firm on "romex is cheap" and scabbing a ground onto an outlet creates an "awkward and hazardous" situation.
One alternative would be to mount one or two multi-gang boxes next to the panel, put in a nipple or two, and run each appropriate circuit's home run through a GFCI device.Running a ground to each receptacle is in my opinion inferior to installing GFCI, however many of those older panels are original, putting in a GFCI breaker in an FPE panel is like polishing a turd, and many of those receptacles are often spidered out from a light box, which would require GFCI receptacles in multiple locations.
That's means you're getting 750ft of conductor. The math is right there. 12/2 has the conductorsIsn't the 12-2 a 250ft roll?
Personal experience on I've hazardous and awkward. Have you ever tried figuring out if that ground wire you ran into that's not in a conduit or cable is actually going somewhere? I have, and found that it's just in the wall going nowhere. Can't fake a working 120v outlet.You still haven't provided any actual support of this claim.
I disagree that running a separate EGC creates a hazardous condition provided it is an effective and low impedance ground path. It does look a little weird, but there is nothing wrong with running a separate EGC... aside from all of the pitfalls I've mentioned above lol.