Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
Contractor wants to put two, single phase 3kVA transformers in line to boost the voltage up then bring it down at the load (120/480V to 480/120V) due to V-drop at 1700+ feet from source. Cable between transformers is 2#6 AWG w/#8 Gnd.There is no primary protection on the second transformer. This seems to be a violation of450.3(B). Contractor says "No" since fault current between the two Xfmrs is not sufficient to cause damage. I don’t see any exceptions that would allow this. Comments?