It's no problem to reverse feed a transformer. 450.11(B) makes this clear. Besides, it's only been recently that the code had anything to say about it at all and I don't think the manufacturers did anything different to their transformers other than add a note to the instructions that says, "It's ok if you want to backfeed this".
Manufacturers vary on this topic. GE says their transformers are capable of stepping up as long as the OCPD is set high enough to handle the inrush current and meet the NEC. Hammond on the other hand states that it would require a special order transformer - same for Eaton Cutler-Hammer.
http://apps.geindustrial.com/publibrary/checkout/Transformer2?TNR=White%20Papers%7CTransformer2%7Cgeneric