Your inspector is most likely going to fall back on NEC 2008 Article 110.2- Approval
the conductors and equipment required or permitted by this code shall be acceptable only if approved
Article 100 - Approved :Acceptable to the Authority having Jurisdiction
If by chance your inspector tries the old stand by 110.3 and not the above then you have a shot at beating him as 110.3 (B) Listed and Labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling;
You equipment IS NOT LISTED so this section does not apply
I've seen many misinterpret 110.3
the conductors and equipment required or permitted by this code shall be acceptable only if approved
Article 100 - Approved :Acceptable to the Authority having Jurisdiction
If by chance your inspector tries the old stand by 110.3 and not the above then you have a shot at beating him as 110.3 (B) Listed and Labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling;
You equipment IS NOT LISTED so this section does not apply
I've seen many misinterpret 110.3