Is it now required to have a commercial 220V oven on a GFCI breaker?
210.8(B) Other Than Dwelling Units. All single-phase receptacles
rated 150 volts to ground or less, 50 amperes or less and threephase
receptacles rated 150 volts to ground or less,
100 amperes or less installed in the following locations shall
have ground-fault circuit-interrupter protection for personnel.
2-pole GFCI cost vs cost of 422.31 disconnect means for hardwired appliances should also be considered.If it isn't direct wired than yes. Kitchen is listed in the section below
If you're merely un-plugging and plugging, nothing need be added.Is it ok to leave 3 wire non GFCI if the oven is just replaced for a new one? this job is a remodel.
If it comes with a flex, do I have to hard wire? If its hard wired I need a disconnect? This customer has documented LOTO does that help?
422.31(B) Appliances Rated over 300 Volt-Amperes. For permanently
connected appliances rated over 300 volt-amperes, the
branch-circuit switch or circuit breaker shall be permitted to
serve as the disconnecting means where the switch or circuit
breaker is within sight from the appliance or is lockable in
accordance with 110.25.
You can use a breaker lock at the panel as the disconnect if it is hard wired
'Thank you Dennis, this is a single phase 220V does the LOTO still apply?
If it comes with a flex, do I have to hard wire? If its hard wired I need a disconnect? This customer has documented LOTO does that help?
2-pole GFCI cost vs cost of 422.31 disconnect means for hardwired appliances should also be considered.
Does not need to be within sight. Must have a locking device on the breaker that complies with 110.25 (must remain in place whether locked or not is the main thing that applies here)So a kitchen subpanel w/in sight of, but not in the kitchen serves well
~S~
So if it’s three wire cord I can just plug the new range in, if it’s a flex is that the same, grandfathered? Just wire it up?the building circuit is three wire,I just want to put the new range in place.nothing with the building wiring.
Yes.The range will come with a flex,no cord, can I just wire it up, making sure to bond the frame?
Right now the range is a 3 wire with a flex, no receptacle, no disconnect no gfci. It is a 1990 building, the new range would be the same, drop in range with flex, no receptacle. would this be the same as just swapping out old range with new? or do we need to change to a 4 wire with a wall disconnect.