how would you go about bonding the metal screws?
Read my previous posts
how would you go about bonding the metal screws?
I read what you said. You claimed that the little screw recess in the box effectively insulates the screw head. I don't see how it does anything of the sort if a wire nut comes loose. The end of the wire can go anywhere.Read my previous posts
I read what you said. You claimed that the little screw recess in the box effectively insulates the screw head. I don't see how it does anything of the sort if a wire nut comes loose. The end of the wire can go anywhere.
One of the problems I have always had with the term "likely" is that the code uses it but never defines it in some useful way.
I admit in 20 years, I almost never bond the fixture bar with a wire
The bracket in the OP is inside of the box and is for mounting a fixture to the box. One of these types:how would you go about bonding the metal screws?
in any case, the mounting bracket is on the outside of the box.
I thought he was talking about the bracket that supports the box into the ceiling. This is more plausible about potentially getting energized.
I don't think the NEC is worried about an internal box mounting screw becoming energized. However, it is concerned about energizing a mounting bracket that could be contacted by a person, such as a luminaire canopy.Of course it can but the nec appears to accept the recess as a safe bet.
Do the 8/32's typically used to mount the fixture to the strap provide a bonding means? Why would the crossbar need a different size egc from the fixture they are part of the listed fixture.
If you use the box that Dennis posted the brach circuit EGC would go to the green screw and the EGC from the fixture would go to the green screw on the fixture bar. They do not need to be spliced together.If I were to use the non metallic box like Dennis posted, then I would not have to make up the fixture egc to the branch circuit egc. (for sake of discussion). I still feel that the 8/32's will provide a bonding means with the box posted or with a standard fiberglass box and metal strap.
So you're saying that you're relying on the fixture to bond the strap?I understand that concept, I guess my logic is on a standard plastic or fiberglass box with out the ground strap. The fixture strap will be bonded to the egc via the 8/32's used to attach the fixture to the strap.
That's a violation. As Dennis stated the EGC must connect to the bar.
250.148(B) Grounding Continuity. The arrangement of grounding connections shall be such that the disconnection or the
removal of a receptacle, luminaire, or other device fed from the box does not interfere with or interrupt the grounding continuity.