Attached pdf shows grounding electrode at the generator which is non separately derived system. Is this okay for non separately derived system?
Not sure why someone would think that an extra ground rod or two would be a big improvement of the existing building GES.
In your sketch their is no ground electrode but in mine their is. I am reading this correct extra electrode on the generator in pdf is ok as long as neutral and ground are not tied together at the generator?The extra electrode is fine. The EGC ties it to the building GES.
Key points are unswitched neutral in transfer switch and note 9 on the drawing.
No supply side bonding jumper at genny.
Separate EGC and neutral from genny to transfer switch.
View attachment 19728
In your sketch their is no ground electrode but in mine their is. I am reading this correct extra electrode on the generator in pdf is ok as long as neutral and ground are not tied together at the generator?