Nonincendive Protection Method in Class 1, Div 2 Locations
u791262
Retired
Is there anyone who might be able to help me with questions concerning Nonincendive Protection Method in Class 1, Div 2 Locations?
1st question
1st question
Should a nonincendive installation always have a "control drawing"?
Yes. Section 501.10(C) and the defintion in 500.2 This hasn't always been true but it has been since ISA has basically taken control of limited energy systems (non incendive and intrinsically safe). ANSI/ISA-12.12.01
Thanks for your reply Bob. I am not finding Sec. 501.10(C) in either the NEC 2008 or 2011 editions. Is it possible you were referring to 501.10(B)(3). Also, since the section I just referred to mentions "simple apparatus", can a Honeywell tach sensor be installed in a Class1, Div 2 location and be considered as nonincendive without a control drawing? My inclination is no. I would think that if you cannot use Class1, Div 2 wiring methods, then to use the sensor, plus the associated wiring that goes into the hazardous location, it would have to be approved by a Third Party Testing Agency (NRTL) to be considered as a nonincendive circuit.
I have no idea how 501.10(C) popped into my head while I was typing :ashamed1: The proper reference is indeed 501.10(B)(3).
Simple Apparatus is defined in Article 504.2.