synchro
Senior Member
- Location
- Chicago, IL
- Occupation
- EE
Look at it like this: "balanced" nonlinear loads on each phase to neutral will produce current, and that current will appear on the primary neutral in proportion to the transformer's voltage ratio.
Now, take those same loads and place them in delta. What happens? Does current appear on the primary neutral?
Obviously there will be essentially no current on a secondary side neutral of a wye-wye with only line-to-line loads, whether they are nonlinear or not.
If the wye-wye is made up of individual single-phase transformers I believe the neutral current on the primary side should also be negligible. For each line-to-line load, all of the current flowing through one phase winding connected to the load will flow back through the other phase winding, resulting in no current from their common neutral on the secondary side. The individual single phase transformers will reflect these same conditions to the primary side, resulting in negligible primary neutral current.
Now if the 3-phase transformer has common cores between phase windings (eg. 3, 4, 5 legs) then there is some coupling between the magnetic flux in the different legs of the cores. And even more so in the 3-leg variety because it's the least symmetrical for magnetic paths. So if there's a line-to-line load between two of the phases there will be some magnetic flux coupled into the core leg for the third phase. This would then cause some current to flow through the primary winding for the third phase, and therefore through the primary neutral. This effect would apply not only to currents at the fundamental 60 Hz frequency but also to harmonics. I don't know what level of neutral current this would cause, and it would obviously depend on the details of transformer construction.