MannyBurgos
Senior Member
- Location
- Waukegan, IL
Realistically, the wire does not need to be larger than the fuses in the disconnect, by the way what size are they?
I would recommend that the overheated lug also be replaced.
Each fuse is 600 amps....
Realistically, the wire does not need to be larger than the fuses in the disconnect, by the way what size are they?
I would recommend that the overheated lug also be replaced.
Yes, especially if they have any demand type metering to prove the load is/has been under the conductor ampacity.im gonna give poco a call on Tuesday to come out and inspect and hand them my load calcs so do you think they will just blow me away?
POCO responsibility is dependent on where the service point is. The fact this is an older install things could have changed from the time of installation to now. There are several ways to splice it, but the splice can't be in the raceway, which is probably a problem for you. However if it is indeed POCO's responsibility to repair (the conductor - the damaged lug/or other components may still be on the owner) they possibly could splice it in the raceway if they wanted as they do not have to follow NEC.Ok. Im going to go with a loose connection and poco wires are undersized which is acceptable to ahj.
This would be a first time repair for me for damage on a service entrance conductor. Is poco responsible for repair on this wire or is customer responsible for this? No slack available to cut and re-install. What's the best way to splice a piece of 350kcmil aluminum while still meeting 2011 Nec?
Can you cite any code reference requiring that?
I would imagine that it is not just any "grease" as for water protection, but instead specifically an anti-oxidant mixture.110.12.B ? Not being a Code guy (most of utility work is non-NEC stuff) I can only go by years of experience with service entrance cable. I've investigated many complaints of flickering lights, dim/bright lights (neutral problem), low voltages, etc. I'd say 90% are due to a loose or corroded aluminum connection that has overheated to the point that service equipment or conductor was damaged. Contact grease seems to have been used only rarely. NEC is minimum requirements. I just always did it that way and still will. All aluminum rated "insulink splices" and Polaris connectors I've seen have grease inside. Must be a reason.
Old aluminum alloys (like from 25+ years ago) did require antioxidation compound. Newer alloys used now do not require it, but it doesn't hurt to use them either. People that were in the trade when those old alloys were all that was available were trained to always use compound, and old habits just kick in automatically. Some of us that have been in the trade 25ish years were trained to always use compound just because that is all those that trained us knew at the time, though most of the new conductors we were handling really did not require use of compound.110.12.B ? Not being a Code guy (most of utility work is non-NEC stuff) I can only go by years of experience with service entrance cable. I've investigated many complaints of flickering lights, dim/bright lights (neutral problem), low voltages, etc. I'd say 90% are due to a loose or corroded aluminum connection that has overheated to the point that service equipment or conductor was damaged. Contact grease seems to have been used only rarely. NEC is minimum requirements. I just always did it that way and still will. All aluminum rated inline splices such as "Insulink" and Polaris connectors I've seen have grease inside. Must be a reason.
That lug is in need of replacement and other damage may exist. Looks like it may have come loose when the wire was installed as the lug is twisted.
POCO should be responsible for the wire , but usually does not take responsibility for the equipment on customer side. At least that is the way on the west coast.
[Old aluminum alloys (like from 25+ years ago) did require antioxidation compound. Newer alloys used now do not require it,]
Back to my comment....Polaris and Insulink devices all still have dielectric compound inside. If it isn't necessary, I really doubt the manufacturers would go to the added expense. Profit margin.....but just my opinion....if yours is different, I'll patiently explain why you're wrong.![]()
I'm not opinionated, I'm just always right!:roll:
Here's one opinion besides mine..AlumiConn connector Mfgr...
Do I Need To Add Antioxidant to the AlumiConn Connector?
I recently got off the phone with a contractor from New Jersey who was asking several good questions about the AlumiConn connector. And one question that came up (that many other people ask, too) is whether or not you need to add antioxidant when you install an AlumiConn connector.
The answer is that you do not need to add any antioxidant to the AlumiConn connector because they already come pre-filled with a proprietary antioxidant sealant that coats the wires as you insert them into the connector!
This proprietary antioxidant helps to dramatically reduce oxidation ? one of the primary problems with aluminum wiring. Oxidation occurs when oxygen comes into contact with metal and is particularly problematic with aluminum as the oxidation occurs faster than with copper. As this oxidation builds up on the wire, it causes more resistance for any electrical current to run through it, which results in heat build up and can possibly cause a fire.
So, it?s extremely important that you use antioxidant when dealing with aluminum wire! And since the AlumiConn connector comes pre-filled with the antioxidant, you can save time and money since you won?t need to buy any additional antioxidant or take the time to install it!
All aluminum rated inline splices such as "Insulink" and Polaris connectors I've seen have grease inside. Must be a reason.
I think you need to strip more insulation off conductors - especially the bottom lead on the breakerJust finished installing the retro.
I think you need to strip more insulation off conductors - especially the bottom lead on the breaker![]()
There are a few inspectors in the Chicago burbs that will give you a red tag if there is more than 1/8" of bare conductor between the lug and the insulation....just an unwritten rule that is enforced in some areas.I think you need to strip more insulation off conductors - especially the bottom lead on the breaker![]()
There are a few inspectors in the Chicago burbs that will give you a red tag if there is more than 1/8" of bare conductor between the lug and the insulation....just an unwritten rule that is enforced in some areas.
.... Upon doing further research on trying to find a replacement assembly, it turns out that this is a common issue with Sylvania GTE panels. Could not find any documentation or parts for that matter for this catalog no. We had to get Power Distribution in Franklin Park, IL. to fabricate a retrofit for us. I literally just got the engineer to bring to job site. Back to work...