Good solution, to meet a pointless requirement. But sometimes you gotta to what you gotta do.Seems like a good solution.
Good solution, to meet a pointless requirement. But sometimes you gotta to what you gotta do.Seems like a good solution.
The City of Austin won't allow splices in panels. AHJ rules, so again...any constructive way around this?
Sent from my iPhone using Tapatalk
Good solution, to meet a pointless requirement. But sometimes you gotta to what you gotta do.
The City of Austin won't allow splices in panels. AHJ rules, so again...any constructive way around this?
Sent from my iPhone using Tapatalk
That rule is not in the city amendments of the NEC.
http://www.austintexas.gov/edims/document.cfm?id=159607
I knew Austin was weird, but never thought they were that weird- op has been misled.
Technicalities make a difference here. According to NEC the panelboard is the assembly containing the bus, it is installed in a "cabinet".
IMO city of Austin is objecting to splices in the cabinet (or did they redefine what a panelboard is vs what the NEC defines it as) and is making up rules that don't fully make any sense - is not possible to splice in the panelboard.
NEC doesn't object to splices in a cabinet.
My question earlier was regarding whether the neutral bus is part of the panelboard or is just another accessory inside the cabinet that also houses the panelboard
?
Also can't one consider to some extent that each neutral termination on that bus is a splice within the "cabinet"?
Set a j-box outside of the panel and make your connections there.
Misled, bamboozled and horn swoggled I'd say.
You know I've not looked in the city's criteria to argue this but both city inspectors and third party inspectors for the Austin real estate market flag it constantly. Normally it's not a problem because there are always extra holes on the bus.
Sent from my iPhone using Tapatalk
City of Austin is crazy about changing things like making sure red is on the left and black is on the right. For high volt they prefer brown yellow purple rather than brown orange yellow. They also make you buy meter cans from them now.
I knew Austin was weird, but never thought they were that weird- op has been misled.
You know I've not looked in the city's criteria to argue this but both city inspectors and third party inspectors for the Austin real estate market flag it constantly. Normally it's not a problem because there are always extra holes on the bus.
Sent from my iPhone using Tapatalk
I also don't see anything in there about double lugging a neutral not being acceptable. Is there anything in the NEC that talks about double lugging a neutral not being an approved method?
Sent from my iPhone using Tapatalk
You can't double up the noodles.
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
Would there be an objection to removing the 2 neutral wires from the bus, inserting a single neutral wire in the bus an bonding that wire to the others 2 together with a wirenut.