Troubleshooting tripping residential GFCI in a garage this AM.
It's about waist high with a couple of boxes in front of it and some golf clubs to the side. It's a little awkward but not as bad as a kit countertop recep.
Wires are all twisted up. Line in pair was identified by the ground wire wrapping around it tightly about 6 times. Two lines out. I decided I didn't like it so I remove the recep and start untwisting the mess. I am aware of the hot wire but didn't take two seconds to put a nut on it.
My hands/arms were in an odd position untwisting the ground and my hand made slight contact with the hot wire. I jerked back and hit myself square in the nose with the back of my hand. My eyes were watering and I could feel the blood starting to trickle.
No one was around to witness this event. I walked to my truck for a paper towel and after about 30 seconds I realized how funny it was.
The problem was a neutral to ground fault in the front patio recep. On installation, the ground wire was probably very close to the 3/8" of exposed neutral on the backstabbed recep. The recep must have shifted over/back a bit when somebody used it.
It's about waist high with a couple of boxes in front of it and some golf clubs to the side. It's a little awkward but not as bad as a kit countertop recep.
Wires are all twisted up. Line in pair was identified by the ground wire wrapping around it tightly about 6 times. Two lines out. I decided I didn't like it so I remove the recep and start untwisting the mess. I am aware of the hot wire but didn't take two seconds to put a nut on it.
My hands/arms were in an odd position untwisting the ground and my hand made slight contact with the hot wire. I jerked back and hit myself square in the nose with the back of my hand. My eyes were watering and I could feel the blood starting to trickle.
No one was around to witness this event. I walked to my truck for a paper towel and after about 30 seconds I realized how funny it was.
The problem was a neutral to ground fault in the front patio recep. On installation, the ground wire was probably very close to the 3/8" of exposed neutral on the backstabbed recep. The recep must have shifted over/back a bit when somebody used it.