Let?s look a little closer to article 220 than some are.
The title is: ARTICLE 220 Branch-Circuit, Feeder, and Service Calculations
This article is broken into five parts as follows:
I. General
II. Branch Circuit Load Calculations
III. Feeder and Service Load Calculations
IV. Optional Feeder and Service Load Calculations
V. Farm Load Calculation
The section of this article in question is Part II which is clearly for Branch Circuit Load Calculations.
Some think that the whole Article addresses services and feeders but this is not true as evidenced by the title of Part II and the first section of Part III.
III. Feeder and Service Load Calculations
220.40 General.
The calculated load of a feeder or service shall not be less than the sum of the loads on the branch circuits supplied, as determined by Part II of this article, after any applicable demand factors permitted by Parts III or IV or required by Part V have been applied.
Right or wrong I teach that the limits outlined in Table 220.12 General Lighting Loads by Occupancy can not be exceeded. Using this method a 15 amp circuit could not cover more than 600 square feet of floor space. (15X120/3)
The title is: ARTICLE 220 Branch-Circuit, Feeder, and Service Calculations
This article is broken into five parts as follows:
I. General
II. Branch Circuit Load Calculations
III. Feeder and Service Load Calculations
IV. Optional Feeder and Service Load Calculations
V. Farm Load Calculation
The section of this article in question is Part II which is clearly for Branch Circuit Load Calculations.
Some think that the whole Article addresses services and feeders but this is not true as evidenced by the title of Part II and the first section of Part III.
III. Feeder and Service Load Calculations
220.40 General.
The calculated load of a feeder or service shall not be less than the sum of the loads on the branch circuits supplied, as determined by Part II of this article, after any applicable demand factors permitted by Parts III or IV or required by Part V have been applied.
Right or wrong I teach that the limits outlined in Table 220.12 General Lighting Loads by Occupancy can not be exceeded. Using this method a 15 amp circuit could not cover more than 600 square feet of floor space. (15X120/3)