Q1 What is the maximum number of 15 or 20A, 125V receptacle outlets permitted on a 20A, 120V general-purpose branch circuit in a commercial occupancy?[/FONT]
[FONT=Arial, Helvetica, sans-serif]
A1 For commercial occupancies, the NEC requires each receptacle outlet to be calculated at 180 VA [220.14(I)]. Therefore, the maximum number on a 20A circuit would be 13. [/FONT]
[FONT=Arial, Helvetica, sans-serif]Circuit VA = Volts x Amperes
Circuit VA = 120V x 20A
Circuit VA = 2,400 VA
Number of Receptacles = 2,400 VA/180 VA
Number of Receptacles = 13[/FONT]