Looking at a job in NYC and all the panel schedules forapartment lighting show a 15A breaker with #14 wire. I’m being told it’s acode(NYC) violation. Anyone familiar with this? Thanks.
SECTION 210.19 Subsection 210.19(A)(1) – Add a new sentence at the end of the paragraph before the first Exception to read as follows: Conductors of branch circuits shall be sized to allow for a maximum voltage drop of 3 percent at the last outlet supplying light, heat or power and the maximum voltage drop allowable for feeders and branch circuit combined shall not exceed 5 percent. FPN No. 4 – Delete the FPN in its entirety.
Subsection 210.19(A)(4) – Revise the first sentence of the paragraph by replacing “14 AWG” with “12 AWG"
SECTION 210.24 Section 210.24 Table – Replace the value “14” that appears twice in the column headed 15A, and once each in the columns headed 20A and 30A in the Circuit Rating Section with the value “12.”
Would someone kingly provide a valid and "logical" reason for such OVER "design"?
RC
As pointed out, it is not the 15A breaker that is the problem, just the #14AWG
Would someone kingly provide a valid and "logical" reason for such OVER "design"?
RC
One thing that comes to mind is old buildings with screw-in Buss fuses where people put the penny behind it so they can plug in more electric heaters.
One thing that comes to mind is old buildings with screw-in Buss fuses where people put the penny behind it so they can plug in more electric heaters.
When were fuseboxes last installed in as a panel? Late 50s, early 60s?
Than why not make it 10 AWG?
Those fuse come in 30s.
It's just a senseless rule likely made by someone with a Tim Taylor bigger is better personality.
I don't see this any different than the NEC forcing us to use a #12 conductor at 20 amps when it's 75°C ampacity is 25 amps.
I don't see this any different than the NEC forcing us to use a #12 conductor at 20 amps when it's 75°C ampacity is 25 amps.
I remember reading on this forum that a branch circuit for a fire alarm panel in NYC must be in 3/4" RMC, #10 XHHW conductors and terminate on a fused disconnect.
We have been installing those in some jobs.
I remember reading on this forum that a branch circuit for a fire alarm panel in NYC must be in 3/4" RMC, #10 XHHW conductors and terminate on a fused disconnect.
You mean other than prohibiting a wire size that works fine everywhere else?
It's dumb and not defendable