Great graphic!!Here is what I think could be happening here, and is probably a oversight of the 2023 NEC;
View attachment 2575666
Great graphic!!Here is what I think could be happening here, and is probably a oversight of the 2023 NEC;
View attachment 2575666
But is the neutral-ground bond in the box with the receptacle? I always thought agree bonding occurred in the appliance.Great graphic!!
But is the neutral-ground bond in the box with the receptacle? I always thought agree bonding occurred in the appliance.
While in school can remember being told that Brooklyn Bridge has over a hundred amps flowing thru it.If piping is in parallel with a neutral path it will carry current, even if said neutral has a good path. Ohm and Kirchoff weren't lying![]()
If it is something doable you would need to connect to something with a 10 AWG grounding conductor since it is a 40 or 50 amp branch circuit, and I'd guess most of what is close by and convenient only has 14 or 12 AWG grounding conductors.One last question I have herd you can run a bare or green ground wire externally and tap off to ground old outlets is this ok to do for a converting a range outlet from a 3 wire to a 4-wire NEMA 14-50?
Thanks everyone for the help, to clarify for those who asked its a 50 Amp 3 wire NEMA 10-50 receptacle that powers the ranges, the ranges have a gas cooktop and electric oven.
It would be quite a job to rewire all the range circuits, and the building owners don't want to spend any money that they don't have to, nor do they want to disrupt the tenants.
One last question I have herd you can run a bare or green ground wire externally and tap off to ground old outlets is this ok to do for a converting a range outlet from a 3 wire to a 4-wire NEMA 14-50?
And this wire is sized for the largest circuit that will be grounded so a #10 bare could do all the ranges?
We'd actually use #8 bare because we have a roll of that.
Thanks again
My boss was informed today that the state of Massachusetts has for a long time opted to delete 250.130(C).Yes, you can do this according to 250.130(C).
Yeah we asked the pipe fitters to do that, they said its an electrical issue citing the NEC 250.6 for objectionable current.Placing dielectric union on gas piping maybe something worth consideration?
Placing dielectric union on gas piping maybe something worth consideration?