Addressing NEC 250.50 and 250.52
I have objectionable net current on a grounding wire to a water meter,
(oscillating) measuring between 2-5.0 amps
with an ammeter causing very high magnetic fields in living areas. I have two separate connections to the copper metallic water pipes
that seem to satisfy the code as far as BONDING and GROUNDING.
One BOND as a copper wire approximately 5-6 feet connecting from electric box to nearest copper pipe/ plumbing
and also a separate copper wire providing a GROUND,
for approximately 25 feet attached to the street-side of water meter
(between meter and street where it enters into concrete wall in basement in NY.)
Background:
There is a grounding rod, and have not measured it?s resistance in Ohms for effectiveness.
My understanding is that even if the resistance was reduced down to 1 ohm,
it would not be the path of least resistance relative to copper pipes/ meter
due to conductivity of soil being inferior to the copper metal.
There is a main water line that runs 6 feet or so along side of this townhouse.
that each unit T's into... wondering if I can make use of this to satisfy code.
Diagram:
--------------------------------------------- Main water line about 6 feet from townhouse
| |
| |
--------------------------------------------- Edge of Building to Basement
| |
water meter Electr Box - with new ground wire to outside Water Liine
About 35 feet between water meter and electric box
Could the ground wire between the electric box and the water meter
that is carrying this current
(since it has the path of least resistance between it and the ground rod)
be removed, and to #1) satisfy bonding, attach a ground wire from the electric box to the closest copper pipe
internally within the basement,
and then #2) use another copper wire to go from electric box to closest OUTSIDE plumbing as a GROUND
which would be that existing main water line I had mentioned.
Essentially re-routing the current outdoors.
In this way the current carried on the previous copper wire path to water meter
would then flow to outside of home to the main water line.
This new path would then carry the current and would radiate fields outside and not inside the house.
WOULD THIS SATISFY CODE or would the code need revision
to allow regulations to meet the goals of both bonding and grounding
without handcuffing us to the locations and distances
of where we need to connect to on these pipes to accomplish this result.
As a side note:
I have also noticed with a gauss meter and with an ammeter,
that a nearby home has currents on their phone and/ or cable line
and they are only 20 feet away from this same home.
Also someone mentioned that this nearby home could have a broken neutral
since walking in front of their house on sidewalk
measures double digit magnetic readings in front of their home.
They also have a metallic box or outlet - outdoor plug
that stakes into ground in landscape that when i approach it
it goes off the charts with magnetic fields on gauss meter
(wiring errors? neutral touching ground or in contact with metallic box?).
Are these all related issues, separate?
I?m trying to isolate this home from the others.
Once I kill the power (mains) in this home that has the ground line carrying the objectionable current,
there about a 80% drop in current with amperage at about 1.0-1.5 that can also be read with an ammeter
at the point of entry with water meter inlet
which tells me there are currents on main water line outside that enters into the dwelling..
So again, would replacing the water meter ground
with a separate copper wire to the water line outside the home
be compliant to satisfy code?
Thanks in advance with any insights that you may have
or any resources or professionals that can help me with these challenges.
Here's a great video explaining the issue that i've found online
https://www.youtube.com/watch?v=U2iejrZsXkM
Only problem is that this solution addresses isolating internal water pipes,
yet not the objectionable current on the grounding line between electric box and water meter.
I have objectionable net current on a grounding wire to a water meter,
(oscillating) measuring between 2-5.0 amps
with an ammeter causing very high magnetic fields in living areas. I have two separate connections to the copper metallic water pipes
that seem to satisfy the code as far as BONDING and GROUNDING.
One BOND as a copper wire approximately 5-6 feet connecting from electric box to nearest copper pipe/ plumbing
and also a separate copper wire providing a GROUND,
for approximately 25 feet attached to the street-side of water meter
(between meter and street where it enters into concrete wall in basement in NY.)
Background:
There is a grounding rod, and have not measured it?s resistance in Ohms for effectiveness.
My understanding is that even if the resistance was reduced down to 1 ohm,
it would not be the path of least resistance relative to copper pipes/ meter
due to conductivity of soil being inferior to the copper metal.
There is a main water line that runs 6 feet or so along side of this townhouse.
that each unit T's into... wondering if I can make use of this to satisfy code.
Diagram:
--------------------------------------------- Main water line about 6 feet from townhouse
| |
| |
--------------------------------------------- Edge of Building to Basement
| |
water meter Electr Box - with new ground wire to outside Water Liine
About 35 feet between water meter and electric box
Could the ground wire between the electric box and the water meter
that is carrying this current
(since it has the path of least resistance between it and the ground rod)
be removed, and to #1) satisfy bonding, attach a ground wire from the electric box to the closest copper pipe
internally within the basement,
and then #2) use another copper wire to go from electric box to closest OUTSIDE plumbing as a GROUND
which would be that existing main water line I had mentioned.
Essentially re-routing the current outdoors.
In this way the current carried on the previous copper wire path to water meter
would then flow to outside of home to the main water line.
This new path would then carry the current and would radiate fields outside and not inside the house.
WOULD THIS SATISFY CODE or would the code need revision
to allow regulations to meet the goals of both bonding and grounding
without handcuffing us to the locations and distances
of where we need to connect to on these pipes to accomplish this result.
As a side note:
I have also noticed with a gauss meter and with an ammeter,
that a nearby home has currents on their phone and/ or cable line
and they are only 20 feet away from this same home.
Also someone mentioned that this nearby home could have a broken neutral
since walking in front of their house on sidewalk
measures double digit magnetic readings in front of their home.
They also have a metallic box or outlet - outdoor plug
that stakes into ground in landscape that when i approach it
it goes off the charts with magnetic fields on gauss meter
(wiring errors? neutral touching ground or in contact with metallic box?).
Are these all related issues, separate?
I?m trying to isolate this home from the others.
Once I kill the power (mains) in this home that has the ground line carrying the objectionable current,
there about a 80% drop in current with amperage at about 1.0-1.5 that can also be read with an ammeter
at the point of entry with water meter inlet
which tells me there are currents on main water line outside that enters into the dwelling..
So again, would replacing the water meter ground
with a separate copper wire to the water line outside the home
be compliant to satisfy code?
Thanks in advance with any insights that you may have
or any resources or professionals that can help me with these challenges.
Here's a great video explaining the issue that i've found online
https://www.youtube.com/watch?v=U2iejrZsXkM
Only problem is that this solution addresses isolating internal water pipes,
yet not the objectionable current on the grounding line between electric box and water meter.