Author's Comment:
Controversy about using metal underground water piping as a grounding electrode has existed since the early 1900s. The water industry believes that neutral current flowing on water piping corrodes hte metal. For more information, contact the American Water Works Association about their report—Effects of Electrical Grounding on Pipe Integrity and Shock Hazard, Catalog No. 90702, 1.800.926.7337. Figure 250-105 Mike's Comment from Grounding and Bonding
American Water Works Association
American Water Works Association
Journal.
American Water Works Association
Peer Reviwed
Electrical grounding, pipe integrity, and shock hazard
Steven .J Duranceau, Melvin .J Schiff, Graham EC.. Bell
First published: 01 July 1998
Abstract
Electrical currents on metallic water service lines and mains affect corrosion of buried metal piping and can result in random shock hazards for water utility employees.
The practice of using metallic water piping as part of the electrical grounding system of a building has been commonplace for more than 80 years. Modern electronics such as variable-speed motors, televisions, and computers produce both direct current and alternating current (AC), which can flow along metallic water service piping. When electrical transformers serve multiple buildings, the water services and distribution piping can act as parallel neutral return paths for AC from building electrical systems to the transformers. AC can increase the rate of corrosion of distribution and service piping and create shock hazards for distribution workers. As long as the current remains on the electrically continuous pipe, corrosion is not affected. Corrosion occurs when current leaves the pipe and flows through the earth.
American Water Works Association
Journal.
American Water Works Association
Peer Reviewed
Effect of Grounding and electrical properties ON WATER QUALITY
Graham EC.. Bel, Steven .J Duranceau
First published: 01 May 2002
https://doi.org/10.1002/j.1551-8833.2002.tb09475.x *
To whom correspondence should be addressed
Abstract
The use of metallic water piping as part of a building's electrical grounding system has been a commonplace practice for more than 80 years. When electrical transformers serve multiple buildings, the water services and distribution piping can act as parallel neutral return paths for stray current from building electrical systems to the transformers. Electrical resistance in pipe connections, fi present, forces some fraction of the stray current to flow through the parallel water path. Discharge of current on the inside of the pipe increases metal release. Previous studies on the effects of grounding on water quality and metal release did not investigate the effects of resistance or dielectric fitting. This study investigated the effects of dielectric fittings on water quality.
Copper tubing that had been modified with inserted dielectric fittings was filled with potable water from two different water sources and was tested with applied alternating current (AC) voltages of up to 123 Vfor periods of up to 110 h. Significant increases in copper, lead, and zinc in stagnant potable water were measured in less than 24 h at
applied voltages of ~50 VAC. Metal release generally increased with charge transfer, in accordance with Faraday's law.