In vetting some exam questions....

4/0 AL 75* conductors on the secondary of a 208Y transformer. What is the maximum OCPD allowed?
The author says it is 200 amp. I say this should be max 175 per 240.21(C).
What say all?
 

templdl

Senior Member
Location
Wisconsin
In vetting some exam questions....

4/0 AL 75* conductors on the secondary of a 208Y transformer. What is the maximum OCPD allowed?
The author says it is 200 amp. I say this should be max 175 per 240.21(C).
What say all?
Have you considered Art 450 table 450.3(A)?
Also, why did you omit the KVA rating of the transformer in your post?
 

Smart $

Esteemed Member
Location
Ohio
In vetting some exam questions....

4/0 AL 75* conductors on the secondary of a 208Y transformer. What is the maximum OCPD allowed?
The author says it is 200 amp. I say this should be max 175 per 240.21(C).
What say all?
Depends on how exhaustive you want to make it.

4/0 AL 75* conductors have an allowable ampacity of 180A. They could be installed in an ambient of 10?C or less, so 180A ? 1.20 correction factor = 216A.

:D
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What exactly did the question ask for? The rules in 450 for the protection of the secondary winding of the transformer are not the same as the rules in 240 for the protection of the secondary conductors.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
What exactly did the question ask for? The rules in 450 for the protection of the secondary winding of the transformer are not the same as the rules in 240 for the protection of the secondary conductors.

I know that and that is why I think the answer of 200 amps is wrong. The question is what is the maximum OCPD for 4/0 AL 75* conductors on the secondary of a Y transformer. In my view 450 rules have nothing to do with the question. 240.21(C) applies. It would not matter what size the transformer is (as long as the transformer is protected per 450 rules). If you only have 180 amps of conductor ampacity on the secondary, the max breaker would be 175 amps (largest standard size).
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would agree, for a transformer secondary with 4/0 AL, 175 would be the correct size
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I know that and that is why I think the answer of 200 amps is wrong. The question is what is the maximum OCPD for 4/0 AL 75* conductors on the secondary of a Y transformer. In my view 450 rules have nothing to do with the question. 240.21(C) applies. It would not matter what size the transformer is (as long as the transformer is protected per 450 rules). If you only have 180 amps of conductor ampacity on the secondary, the max breaker would be 175 amps (largest standard size).
Correct, but when I see "transformer secondary" I only think of 450. If you want me to think of Article 240, you need to use the term "transformer secondary conductors".

I know that what was posted did not give enough information to get the correct size of the transformer secondary OCPD, but we have not seen the complete question. Often questions are written with information that had nothing to do with the correct answer to the question.
 

templdl

Senior Member
Location
Wisconsin
Correct, but when I see "transformer secondary" I only think of 450. If you want me to think of Article 240, you need to use the term "transformer secondary conductors".

I know that what was posted did not give enough information to get the correct size of the transformer secondary OCPD, but we have not seen the complete question. Often questions are written with information that had nothing to do with the correct answer to the question.

Exactly. To my point of my previous post.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In vetting some exam questions....

4/0 AL 75* conductors on the secondary of a 208Y transformer. What is the maximum OCPD allowed?
The author says it is 200 amp. I say this should be max 175 per 240.21(C).
What say all?

I agree assuming what the actual question was asking but as Smart pointed out vague questions can have many answers.
 

templdl

Senior Member
Location
Wisconsin
I agree assuming what the actual question was asking but as Smart pointed out vague questions can have many answers.

Yes, should the OP include all the necessary information most question could be addressed in a reply or two.
But, it's a lot more fun the guess and to make assumptions on what the OP is trying to ask which is all to familiar.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It is a mystery to me why you all are making such a big deal out of this. It is a simple question and it has enough info to answer the question. Why not just look at the question and answer based on the info given. This has nothing to do with the size of the transformer and article 450. That I thought that would be obvious, but evidently you all have such egos that you can't see the forest for the trees.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Yes, should the OP include all the necessary information most question could be addressed in a reply or two.
But, it's a lot more fun the guess and to make assumptions on what the OP is trying to ask which is all to familiar.

Gee, forgive for not including all the info you deem necessary. I didn't think I need to state the obvious.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Correct, but when I see "transformer secondary" I only think of 450. If you want me to think of Article 240, you need to use the term "transformer secondary conductors".

I know that what was posted did not give enough information to get the correct size of the transformer secondary OCPD, but we have not seen the complete question. Often questions are written with information that had nothing to do with the correct answer to the question.

Condescending nonsense. I'll think long and hard before I continue around here.
 

Smart $

Esteemed Member
Location
Ohio
Condescending nonsense. I'll think long and hard before I continue around here.
Ahh... come on now. Lighten up... please. I consider you a valuable member of this forum. :happyyes:

I've been avoiding additional posts to this thread simply to avert getting anyone to this point. I apologize for those that haven't the foresight or the respect.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Condescending nonsense. I'll think long and hard before I continue around here.

The title of the thread is "OCPD for transformer secondary". The body of the OP does not exactly match the title...I have no idea what the actual question was.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
It is a mystery to me why you all are making such a big deal out of this. It is a simple question and it has enough info to answer the question. Why not just look at the question and answer based on the info given. This has nothing to do with the size of the transformer and article 450. ....

It's a good question - a bit trickey, but still good. As noted, "transformer secondary" pulls one toward art. 450.

Transformary secondary conductors should lead one back to 240.21.C - as you pointed out in post 1.

And, of course as noted by jumper, 240.21.C does not allow upsizing per 240.4.B.

....That I thought that would be obvious, but evidently you all have such egos that you can't see the forest for the trees.
Oh No. Tell me it's not so.:eek: Where could you possibly have gotten that from? :rotflmao:

ice
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It is a mystery to me why you all are making such a big deal out of this. It is a simple question and it has enough info to answer the question. Why not just look at the question and answer based on the info given. This has nothing to do with the size of the transformer and article 450. That I thought that would be obvious, but evidently you all have such egos that you can't see the forest for the trees.