OCPD, next size up (next two size up)
de2
Newark, NJ
If my load is 10AMP and it is continuous load;
10*1.25 = 12.5Amp
Conductor, #12 and OCPD 15A.
Is this a NEC violation if I use 20A OCPD on this circuit? (next two size up)
10*1.25 = 12.5Amp
You can use any OCPD you want as long as your conductors are protected by it.
It depends on what your load is.
Does it have a MOCP (max overcurrent protection rating)?
Or is it a receptacle?
Either could change the answer.
I also believe motors have a limit to the rating of the circuit OCP. So do xformers.
Scenario 1) Load is receptacle?
Scenario 2) Load is commercial kitchen hot bar?
Scenario 3) Lighting circuit?
Scenario 4) Motor, I know the answer this. NEC 430.54
1) Can you plug a lamp with a 60W bulb into a 20A general purpose circuit?
2) Depends.Hard wired or corded equipment?
3) Can you put just two 100W fixtures on a 20A circuit?
Are you worried about overloaded or underloaded circuits?
Here is where question came, i have a 10amp continous load and I hate to use 15amp ocpd with #12awg. I want 20amp ocpd s i the panel so incase if load changes at least 20amp is the standart in that panel.
So 10 amp continous, 1.25= 12.5 amp calculated hard wired commercial kitchen equipment and I want to go 20amp ocpd.
Sent from my SM-G892U using Tapatalk
What is the MOCP on the equipment?
What you mean fuse it? Add a fused disconnect switch beomfore the load? Thats extra cost
Letw do this, load 1, 10 amp, hot bar, non continous, and load 2, 5 amp non continous.
I want to put these two on a same single phase circuit, ocpd.
Can i use 20 amp ocpd or do I have to use 15 amp ocpd?
You cannot put a piece of equipment on a circuit that exceeds the MOCP rating.
What do you mean? I got 15 amp total load and I am using #12 awg. I want to use 20amp ocpd.
Are you saying run 2 branch circuit to each load?
Manufacturer data is not for MOCP, it is for load current value, i think there you misunderstand.