Re: Odd multiwire circuit
Jim Pauley, forgive me should I mess up as I shall try to remember the very words that you used when you explained this to me. Mr. Pauley is on panel 2 which wrote this article.
210.52(B)(1) requires all receptacles located any where in the kitchen, pantry, breakfast room, dining room, or similar area to be on a 20 ampere small appliance circuit with the exceptions of the receptacle outlet for refrigeration, an electric clock, supplemental equipment and lighting on gas-fired ranges, ovens, counter-mounted cooking units, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1 and individual branch circuits that supplies only one utilization equipment.
A lot of confusion about the installation of other receptacle outlets protected by 15 ampere over current devices revolves around the misunderstanding of section 210.52(B)(1). What I will do in order to help with this understanding is break this section down leaving one word on a line by itself.
210.52(A)(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets
covered
by 210.52(A), all countertop outlets
covered
by 210.52(C), and receptacle outlets for refrigeration equipment.
By using the word
covered instead of required it leaves this section to be all encompassing of any and all receptacle outlets that are installed in these locations. Should the word ?required? have been used instead of ?covered? then one or more 15 amp circuit could be installed.
I hope I did a good job of pointing out what he explained to me. I also beg the forgiveness of those that I so rigorously defended the 15 amp circuit against. I am now convinced that I was wrong in my thoughts and now stand corrected.