'service conductors' describe unfused conductors from a TN-C electrical source.There is no Utility. So 250.24 and 250.30 are garbage.
The concept of a 'service' or utility service is outdated and 250.24 should be reworded to clarify what it really covers, a transition form a using the neutral as a protective conductor and a current carrying conductor (TN-C) to a TN-C-S system where the neutral is just a current carrying conductor. As you don't have a TN-C source, you have no need to use a neutral as a equipment ground, so if your running split phase 120/240 you just have a 4-wire TN-S system everywhere.
And you create one GES and connect it to the neutral one time at one place.