Hmm. If you have no service, and just one electrical source, it is by definition an SDS.
If you have no service, and two electrical sources, then you have 0 or 2 SDSs. 0 SDSs would be the case where the two sources have a solidly connected circuit conductor, e.g. the grounded conductor. While 2 SDSs would be the case where there is no non-grounding/bonding connection between the two sources. ...
Lol there you have it. 250.4 thru 250.20 apply, but 250.24 and 250.30 do not. Notably, 250.142(B) also does not apply because of how it’s worded. So, codewise you can ground this system anyway and anywhere you want that meets the very generally stated intents in 250.4.
I would still go with the main panel myself. Keep it simple.
I'm pretty sure the Sol-Ark inverter syncs with the generator when it turns it on. I believe it will not behave like a grid-tied inverter in this configuration, but is capable of acting as a parallel voltage source. As Birken will tell you this is not a particularly new. Actually I'm just assuming it has similar capabilities to the old Trace or Sunny Island.