Good comments on 'Betty-Lou" and space heaters.
Here is an example and case history indicating a 'beyond code' factor that train drivers should consider.
The EU controls what PF and harmonics a load can be, so most electronics being sold in Europe have PFC circuits. Neither the code or USA laws govern PF or harmonics. May have missed some regulations in the last ten years though as have not bothered to keep up being mostly retired old fart?
Anyway, this case history was in early 1990s when entire office buildings first saw computer installations. Indicates the train driver should have put a scope on one of the new computers and looked at the waveform.
Building supplied by a delta-wye transformer on the rooftop. Nearly a thousand new computers and CRT monitors distributed to workers in February.
If train driver had looked at input current waveform, she (notice I assumed it could have been a female :happysad would have noticed the current spikes indicating the computers had simple diode bridges for the CPU power supplies.
Existing cubicles took into account a percentage of "Betty-Lou" heaters, etc. in offices/cubicles. IIRC every office had it's own 20 A breaker an one 20A circuit for each 4 cubicles.
So, summer time comes around and the delta-wye transformer on the roof burns up on the first hot day.
Why? Obvious to those skilled in the art but maybe not to those who simply 'follow the code', the 3rd and 9th harmonics produced by the diode bridges in all the computers ran around in a circle in the delta overheating it. Nothing to do with overall kVA, simply that harmonics of the massive non-linear loads and resultant harmonics.
Kapow.
Here is an example and case history indicating a 'beyond code' factor that train drivers should consider.
The EU controls what PF and harmonics a load can be, so most electronics being sold in Europe have PFC circuits. Neither the code or USA laws govern PF or harmonics. May have missed some regulations in the last ten years though as have not bothered to keep up being mostly retired old fart?
Anyway, this case history was in early 1990s when entire office buildings first saw computer installations. Indicates the train driver should have put a scope on one of the new computers and looked at the waveform.
Building supplied by a delta-wye transformer on the rooftop. Nearly a thousand new computers and CRT monitors distributed to workers in February.
If train driver had looked at input current waveform, she (notice I assumed it could have been a female :happysad would have noticed the current spikes indicating the computers had simple diode bridges for the CPU power supplies.
Existing cubicles took into account a percentage of "Betty-Lou" heaters, etc. in offices/cubicles. IIRC every office had it's own 20 A breaker an one 20A circuit for each 4 cubicles.
So, summer time comes around and the delta-wye transformer on the roof burns up on the first hot day.
Why? Obvious to those skilled in the art but maybe not to those who simply 'follow the code', the 3rd and 9th harmonics produced by the diode bridges in all the computers ran around in a circle in the delta overheating it. Nothing to do with overall kVA, simply that harmonics of the massive non-linear loads and resultant harmonics.
Kapow.