steelersman
- Lake Ridge, VA
so you ran #2 AL or #4 CU?No, but I did run a properly sized 100 amp feeder to a sub panel. The inspector was wondering why the wire was so big.![]()
sorry for jumping the gun Peter.I'm suing you for copying my post.
I'm going off of 310.15 (B)(6)I don't believe either of those would be allowed for a sub-panel.
#4 CU rated at 85-amps
#2 AL rated at 90-amps
per table 310.16 75c
1/0 AL ser
#3 cu?????so you ran #2 AL or #4 CU?
well if we're talking about SER then #4 CU would work#3 cu?????
Yes, I got lazy and left that out.You guys are both missing the boat.....
Do mean not allowed in reference to a 100 amp subpanel??
FYI, SER isn't 75 degree....
Lou is right, 310.15(B)(6) cannot be applied to the sub-panel.I'm going off of 310.15 (B)(6)
I'd have pulled a 14-3 anyway, Scott. People are fickle.
Only on the service if it is larger than 100a you would have to use 3s. I will guess the service Scott put in was larger than 100. This is a subpanel.well if we're talking about SER then #4 CU would work
I didnt know that Mass was on 2008 code maybe you know better. We will see...No on two counts: If he used CU SER, then he would have had to use #1 CU SER, under the 2008 NEC.
If the feeder were between the service and a panelboard that served the entire dwelling unit, he would be able to use the table. It doesn't apply only to service conductors.
As of 01/01/2008.I didnt know that Mass was on 2008 code maybe you know better. We will see...
As of 01/01/2008.
Hey Scott did you use 1s CU??? Or 3s?? be honest
1/0 AL ser
Why wait around for NM when SER is readily available?quoqueelectric said:Wait a minute here why SER for a subpanel why not just nmb?? I smell a rat!
From above:
Why wait around for NM when SER is readily available?![]()