Oh, we forgot to mention the disposal??

Status
Not open for further replies.
I'm going off of 310.15 (B)(6)

That is limited to "3-wire, single-phase service-entrance conductors, service-lateral conductors, and feeder conductors that serve as the main power feeder to each dweeling unit..... For application of this section, the main power feeder shall be the feeder between the main disconnect and the panbelboard that supplies, either by branch circuits or by feeders, or both, all the loads that are part or associated with the dweeling unit."

Since it is a sub-panel, it does not feed all the loads and cannot be used for the wire sizing.
 
You guys are both missing the boat.....







Do mean not allowed in reference to a 100 amp subpanel??
Yes, I got lazy and left that out.
FYI, SER isn't 75 degree....

I looked for the code section on the rating and didn't see it, can I get some help?

Edit: Found it. 338.10(B)(3) which leads you to 334.80 which limits it to 60c. Thanks for heads up.
 
Last edited:
I suppose I should temper my statement with the fact that I haven't seen the house in the flesh, don't know how much wire would have been involved (really don't know the price difference in wire right now anyway), etc.

If it would have cost me an entire roll of 14/3 vs. 14/2, I wouldn't be so bold as to make that statement, I mean.
 
Only on the service if it is larger than 100a you would have to use 3s. I will guess the service Scott put in was larger than 100. This is a subpanel.

No on two counts: If he used CU SER, then he would have had to use #1 CU SER, under the 2008 NEC.

If the feeder were between the service and a panelboard that served the entire dwelling unit, he would be able to use the table. It doesn't apply only to service conductors.
 
No on two counts: If he used CU SER, then he would have had to use #1 CU SER, under the 2008 NEC.

If the feeder were between the service and a panelboard that served the entire dwelling unit, he would be able to use the table. It doesn't apply only to service conductors.
I didnt know that Mass was on 2008 code maybe you know better. We will see...
 
From above:



Why wait around for NM when SER is readily available? :confused:

Why use SER unless it is for a service?? As in Service Entrance Romex meaning you needed a main breaker at the drop and now you are feeding the main service panel with SER. Everything past that is nm we are talking about a subpanel off the main service. It should be nm not service entrance cable.
 