However some areas require a disposal by Code, if so you might have to explain yourself on that one.
...The fun will be when someone argues that point in a municipality that has, by ordinance, outlawed disposals. :smile:
...Scott has opted to violate the code rather than to run a new circuit and bill for it appropriately.
ok you got me. I guess I was wrong. But scott didn't need to use 1/0. He could have used #1 AL. What is a dweeling?That is limited to "3-wire, single-phase service-entrance conductors, service-lateral conductors, and feeder conductors that serve as the main power feeder to each dweeling unit..... For application of this section, the main power feeder shall be the feeder between the main disconnect and the panbelboard that supplies, either by branch circuits or by feeders, or both, all the loads that are part or associated with the dweeling unit."
Since it is a sub-panel, it does not feed all the loads and cannot be used for the wire sizing.
How is it being perfect?
It must not be that fun because you always seem to be in a sour mood.![]()
What's to stop the HO from overloading a circuit after the electrician did his job?
What is a dweeling?![]()
Ivsenroute ,Scott has opted to violate the code rather than to run a new circuit and bill for it appropriately.
ok you got me. I guess I was wrong. But scott didn't need to use 1/0. He could have used #1 AL.
wasasparky said:Did Scott violate the code? or did the homeowner?......
........
Under sink I have duplex for dishwasher on 15 amp circuit.
Disposal name plate says 10.2 amps. DW says max 9 amps.
There is absolutley no new circuit going in woth out major holes, patching and repainting.
What would you do?? ........
The 9 amp dw never went above 6 amps and when it was just runing through the cycle was just over 2. The higest combined ampere total was under 11 amps.
Plug 'em in....Done.
......The bottom line, reality in place of code, as I said the nameplates are way overinflated. There is no issue woth these two appliances sharinga 15 amp branch ciruit and that is how it's staying.
M.D. said:Forgive me fellas,. for what I am about to do,... I am about to install an Individual branch circuit feeding an outlet for a little , old lady's air conditioner,.. and I intend to commit a violation of the Sacred Scratchings. It is purely based on the cost,.. her panel is pushmatic and she is poor... and quite frankly,.. so am I .. there will be no AFCI.
I am prepared fellas, for any act of contrition you so dispose upon me ...just not sit ups ,...I hate doing sit ups.. and oh yeah I can only do about 40 push ups in a row ,... and my knees don't allow for running any longer ,.. reading perhaps??,.. 210.12,... say 100 times ???
__________________
I violated the code. I put the cords on both appliances and I plugged both of them in. Whoopee.
But seriously, you are welcome in my glass house anytime. Just don't throw stones. Oops...too late.
not quite. I'm not in New England and I'm also with Scott on this. It's no big deal to plug them both into the same circuit. Worse that should happen is the breaker trips if it can't handle the load, but it sounds like that won't be an issue.You guys kill me, but at least its entertaining... I'm with Scott all the way on this one.... must be a New England thing.
Does this mean we cut some slack to the DIYs? :smile:
I'm with Scott all the way on this one.... must be a New England thing.
AND if we ASSUME all this in our bid, who ends up getting the job?