GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Got ya


Sent from my iPhone using Tapatalk
The other way to get it, which I find easier to remember, works as follows for a 208Y/120 source:
If each line current is I, and is in phase with the line to neutral voltage, then the power is I x 120 x 3, since there are three line conductors.
But since 208 is equal to 120 x sqrt(3), the above is also equal to I x 208 x sqrt(3). (Since by definition sqrt(3) x sqrt(3) equals 3.)

The final step is to note that the power into a three phase load is not dependent on whether the source is delta or wye.
:)

Sent from my XT1585 using Tapatalk
 

Sahib

Senior Member
Location
India
50f0316258fec4c91c673dd55d3a8dee.jpg


It was just like this, with a ohms law circle for help...


Sent from my iPhone using Tapatalk
One basic assumption of your test is the circuit is linear for application of ohm law.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170708-1357 EDT

Sahib:

mivey is correct.

Further the instantaneous product of voltage and current producing instantaneous power applies to any waveform and any load, linear or non-linear. This product may vary from + to 0 to - from one instant to another.

If you integrate this product over time T, and divide that by T, then you have the average power over T. What would be read on a wattmeter. And that is how a wattmeter works.

If you have a cyclic process, then you might like to make T equal to one cycle, or an integer number of cycles.

If you have a random process, such as white noise, then you want to make T long enough so that your error is less than some desired or tolerated value.

When your process is non-stationary, stationary is a statistical term, then pick a value of T that produces some adequate result. For power line monitor this might be 1/60 second, but that produces a huge amount of data. The original TED system (The Energy Detective) used one second, and even that is a lot of data. Power line data is not stationary.

.

.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
170708-1357 EDT

Sahib:

mivey is correct.

Further the instantaneous product of voltage and current producing instantaneous power applies to any waveform and any load, linear or non-linear. This product may vary from + to 0 to - from one instant to another.

If you integrate this product over time T, and divide that by T, then you have the average power over T. What would be read on a wattmeter. And that is how a wattmeter works.

If you have a cyclic process, then you might like to make T equal to one cycle, or an integer number of cycles.

If you have a random process, such as white noise, then you want to make T long enough so that your error is less than some desired or tolerated value.

When your process is non-stationary, stationary is a statistical term, then pick a value of T that produces some adequate result. For power line monitor this might be 1/60 second, but that produces a huge amount of data. The original TED system (The Energy Detective) used one second, and even that is a lot of data. Power line data is not stationary.

.

.

I was thinking more along the lines of visualizing the voltage and current waveforms on an oscilloscope. A phase shift would change the result of V x I at any instant and time, which I presumed would be equal to real power.

That is to say, I would think that with a resistive load, Vinst x Iinst = Vrms x Irms, wheras that would not be true with a reactive component.
 

Carultch

Senior Member
Location
Massachusetts
I was thinking more along the lines of visualizing the voltage and current waveforms on an oscilloscope. A phase shift would change the result of V x I at any instant and time, which I presumed would be equal to real power.

That is to say, I would think that with a resistive load, Vinst x Iinst = Vrms x Irms, wheras that would not be true with a reactive component.

When one uses RMS values for voltage and current, they are using a specialized average calculation that acts as a representative value for the waveform as a whole. The special case of a resistive load is such that average power (an actual time average) = RMS voltage * RMS current.

It is true that the instantaneous product of V and I will equal the instantaneous power drawn from the circuit by the component. For energy storage components like capacitors and inductors, there is instantaneous power that is both positive and negative, indicating storage and release. The net time average power for an ideal inductor or capacitor is zero, and all power is reactive. If there is resistance involved as well, there will be a net release of power that is converted into heat. The time average of this net release per cycle, is the real power. The energy stored and released cyclically, is the reactive power.
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
The difference between sqrt3 and 1.732 (sqrt3 to 3 significant digits)

[sarcasm mode]
My math teacher called that 4 significant digits.

sqrt3 ~ 2 (1 significant digit)
sqrt3 ~ 1.7 (2 significant digits)
sqrt3 ~ 1.73 (3 significant digits)
sqrt3 ~ 1.732 (4 significant digits)

[/sarcasm mode]

but this has nothing to do with your excellent point, just one of my peeves like dampen and dampening vs the correct damp and damping
 

Besoeker

Senior Member
Location
UK
[sarcasm mode]
My math teacher called that 4 significant digits.

sqrt3 ~ 2 (1 significant digit)
sqrt3 ~ 1.7 (2 significant digits)
sqrt3 ~ 1.73 (3 significant digits)
sqrt3 ~ 1.732 (4 significant digits)

[/sarcasm mode]

but this has nothing to do with your excellent point, just one of my peeves like dampen and dampening vs the correct damp and damping
And most calculators have a sqrt function anyway.
 

Sahib

Senior Member
Location
India
Further the instantaneous product of voltage and current producing instantaneous power applies to any waveform and any load, linear or non-linear. This product may vary from + to 0 to - from one instant to another
.

.
That is not disputed. What is disputed is the unit for product of instant voltage and current. I say it is VA. KBMHZ says it is watt applicable for any circuit.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170709-1104 EDT

Sahib:

I am in agreement with K8MHZ. The unit of instantaneous power is watt. And this can be +, 0, or -.

The word power describes doing work, for example raising a weight, or generating heat, and the unit for this has been watt for a rather long time.

.
 

Sahib

Senior Member
Location
India
Sorry wrong.

170709-1104 EDT

Sahib:

I am in agreement with K8MHZ. The unit of instantaneous power is watt. And this can be +, 0, or -.

The word power describes doing work, for example raising a weight, or generating heat, and the unit for this has been watt for a rather long time.

.
Well, in that sense my contention is the product of instantaneous voltage and current need not be always 'power'.:)
 

mivey

Senior Member
I was thinking more along the lines of visualizing the voltage and current waveforms on an oscilloscope. A phase shift would change the result of V x I at any instant and time, which I presumed would be equal to real power.

That is to say, I would think that with a resistive load, Vinst x Iinst = Vrms x Irms, wheras that would not be true with a reactive component.
Vinst x Inst with a resistive load creates a sinusoidal waveform that is above the zero axis (for a sinusoidal input) . It is a sub-cycle consideration.

Vrms x Irms is constant because it looks at an average across the complete cycle (for the resistive load we leave out the pf).

With a mixed load, the reactive components cause the instantaneous power trace to cross the zero axis. The portion below the axis indicates there is reactive power going back and forth over a complete cycle (that cycles equally above and below the zero axis).

Remove that reactive power portion and you are left with an instantaneous power wave that traces above the zero axis and the average over the cycle is what we call the real power we get from Vrms x Irms x power factor.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Well, in that sense my contention is the product of instantaneous voltage and current need not be always 'power'.:)
In the sense of physics, the product of instantaneous current and voltage is a rate of change (flow) of energy. That, by definition, is power. It is not average power or reactive power. It is the current time value of power.
It is only when you integrate it over time that you get energy. Total energy over a time period divided by the time gives average power, which is inherently real power.
When you try to multiply some measure of the periodic current and the periodic voltage, you have thrown away information and may not have a valid measure of average power. In those cases we refer to that numeric product as VA.

Sent from my XT1585 using Tapatalk
 

Carultch

Senior Member
Location
Massachusetts
The unit for this has been watt for a rather long time.

Interestingly enough, the man who is the namesake for the unit of Watt, never even used it. James Watt coined the horsepower unit, which measures the same concept. The SI unit of the Watt wasn't a concept until after his death. The same is true for Jimmy Joule, the namesake of the energy unit the Watt is based upon, as well.
 

Sahib

Senior Member
Location
India
In the sense of physics, the product of instantaneous current and voltage is a rate of change (flow) of energy. That, by definition, is power. It is not average power or reactive power. It is the current time value of power.
It is only when you integrate it over time that you get energy. Total energy over a time period divided by the time gives average power, which is inherently real power.
When you try to multiply some measure of the periodic current and the periodic voltage, you have thrown away information and may not have a valid measure of average power. In those cases we refer to that numeric product as VA.

Sent from my XT1585 using Tapatalk