170708-1611 EDT
Sahib:
PF = Average Real Power consumed in said load over a time T/Vrms*Irms
where Vrms and Irms are individually averaged over the same time T, and
the load is a stationary process
Power factor by definition involves time average values, instantaneous power involves no time factors.
Instantaneous power, v(t)*i(t), is what it is, and it can not tell you how much average power is consumed in some resistive portion of a load over some averaging time. Integration of instantaneous power over some time T is required to obtain total energy to the load over that time T, and dividing by T gives you average power for that time.
I have never seen a definition of power factor on an instantaneous basis. Of what useful value would it have?
.
Sahib:
Power factor of a two terminal load is defined as:Interestingly, in a circuit with inductance or capacitance or both and resistance in series, multiplication of power factor into the product of the circuit instantaneous voltage and current will yield the instantaneous power dissipated in the resistance.
PF = Average Real Power consumed in said load over a time T/Vrms*Irms
where Vrms and Irms are individually averaged over the same time T, and
the load is a stationary process
Power factor by definition involves time average values, instantaneous power involves no time factors.
Instantaneous power, v(t)*i(t), is what it is, and it can not tell you how much average power is consumed in some resistive portion of a load over some averaging time. Integration of instantaneous power over some time T is required to obtain total energy to the load over that time T, and dividing by T gives you average power for that time.
I have never seen a definition of power factor on an instantaneous basis. Of what useful value would it have?
.