ibew441dc
Senior Member
Wireguru is Correct!
Wireguru is Correct!
I stand corrected, thank you wireguru. Now I am curious if there are any other areas in the NEC that would allow this.
Most of the time it is illegal to bury cord, except for applications such as those found at Carnivals, Circuses, Fairs, and Similar Events.
Wireguru is Correct!
not always.....off the subject but 525 allows it at carnivals. I guess the thought there, is the cord is buried for a weekend not a year of heavy equipment driving over it.
ARTICLE 525
Carnivals, Circuses, Fairs,
and Similar Events
III. Wiring Methods
525.20 Wiring Methods.
(G) Protection. Flexible cords or cables accessible to the
public shall be arranged to minimize the tripping hazard
and shall be permitted to be covered with nonconductive
matting, provided that the matting does not constitute a
greater tripping hazard than the uncovered cables. It shall
be permitted to bury cables. The requirements of 300.5
shall not apply.
I stand corrected, thank you wireguru. Now I am curious if there are any other areas in the NEC that would allow this.
(the statement I made was false)Quote-IBEW441dc
It is always illegal to bury cord, even in a raceway.